Hi,

I have got to split some more tails etc and pop a mini consumer unit in someone's meter cupboard.

I always put IP rated consumer units in, you know, just 2 way etc.

Is it really necessary or would you say putting a normal metal clad unit it would be ok? Its just this time I have got to terminate some SWA into it and it would be a lot easier if I could just terminate it into the metal one thats all.

Whats your thoughts on it?
 
I would put an outdoor rated garage unit in such a place, usually IP65. Although the cabinet is gong to be IPX4 rated at least, it could still be subject to condensation from the temperature encountered outdoors. It's going to be the cheaper option I would have thought anyway. As for SWA termination, you should be fine and dandy.
 
Hi,

I have got to split some more tails etc and pop a mini consumer unit in someone's meter cupboard.

I always put IP rated consumer units in, you know, just 2 way etc.

Is it really necessary or would you say putting a normal metal clad unit it would be ok? Its just this time I have got to terminate some SWA into it and it would be a lot easier if I could just terminate it into the metal one thats all.

Whats your thoughts on it?

I don't think many DNO's like the idea of having a CU, mini or otherwise in a cabinet housing their service cut-out and meter installation!! They are normally fine with a consumers switch fuse, but a CU is pushing it...
 
Customers owns the OMB but generally it's accepted that only the DNO's equipment is on the meter board internally as well as externally. Yes it has been done before, but sods law they might tell you to remove it. Having said that I doubt anyone seeing it would give a damn!
 
Usually I would not put one in, but...

This particular house has three cupboard, one electric, another elctric and one gas.... see photos...

So I don't see the harm in using the middle one quite honestly.

And why its like this? I have no idea, it makes no sense, the CU is about 1 meter up and a bit to the left from where the what do you m'call it is. So there are three boxes and this is the middle one. The only explanation I can put on it is, its a cock up. Its got 100A fuse supposedly and 25mm tails, and they go into this, and the 16mm twin an dearth feeds the main house consumer unit.

Oh and house, its about 5 years old. The mind boggles.

2015-01-05 11.56.45.jpg
 
Usually I would not put one in, but...

This particular house has three cupboard, one electric, another elctric and one gas.... see photos...

So I don't see the harm in using the middle one quite honestly.

And why its like this? I have no idea, it makes no sense, the CU is about 1 meter up and a bit to the left from where the what do you m'call it is. So there are three boxes and this is the middle one. The only explanation I can put on it is, its a cock up. Its got 100A fuse supposedly and 25mm tails, and they go into this, and the 16mm twin an dearth feeds the main house consumer unit.

Oh and house, its about 5 years old. The mind boggles.

View attachment 27497

I may be wrong but it looks like the DNO wouldn't allow the switchfuse on their board, so rather than siting it internally they have fitted another standard electric meter cabinet to house it. As far as the DNO will be concerned as the board in there is not theirs you can mount what you want. I would go with your initial thought of metal clad to terminate swa as long as the cabinet and door is in good nick. At the end of the day if you don't your going to have a metal adaptable box anyway to terminate.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Market Harborough

Thread Information

Title
Level of IP for unit within meter cupboard
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
14
Unsolved
--

Advert

Thread statistics

Created
uksparks,
Last reply from
driverman,
Replies
14
Views
2,645

Advert

Back
Top