During an EICR meter tails were found entering the cavity and coming down a stud wall to a consumer unit about 5 meters (direct distance) away.
they do have an isolator but no rcd or other protection .

as cables buried in a wall have to have (RCD) Residual Current Device at 30mA and generally tails over 3 meters are not permitted by DNO ,how can this comply?
 
20220905_120108.jpg
 
As above I hate meter tails being snaked through a wall cavity or run up inside a stud wall with no way of knowing where they are actually sited

Made even worse if there is no RCD protection
 
Are the tails definitely bare in the stud wall, or is it possible they have mechanical protection, complying with 522.6.204, (which I think would mean no RCD req'd)?

I have come across this a few years back in a new build, when putting up a cabinet in a toilet. The tails were installed in a steel stud wall, and my magnet picked up the mechanical protection. Thinking it was just another steel stud, I tried drilling it for a couple of minutes, before realising something was amiss and checked the other side of the wall to find the CU there!
 
During an EICR meter tails were found entering the cavity and coming down a stud wall to a consumer unit about 5 meters (direct distance) away.
they do have an isolator but no rcd or other protection .

as cables buried in a wall have to have (RCD) Residual Current Device at 30mA and generally tails over 3 meters are not permitted by DNO ,how can this comply?
As @Pretty Mouth has said in his post. I have twice now installed tails like this, both times I have used mechanical protection (3mm steel) which may not be visible without chiselling a bit of the wall out.
 
During an EICR meter tails were found entering the cavity and coming down a stud wall to a consumer unit about 5 meters (direct distance) away.
they do have an isolator but no rcd or other protection .

as cables buried in a wall have to have (RCD) Residual Current Device at 30mA and generally tails over 3 meters are not permitted by DNO ,how can this comply?

Cables buried in a wall don't have to have RCD protection, they can have other forms of protection.

As you are carrying out an EICR it is very difficult to confirm whether or not correct protection has been installed. Examination of cables buried within walls, under floors etc is a standard limitation.

You need to make a judgement call as to whether it is likely to comply or not. When was it installed, what is the general standard of the installation, what records are available?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

newfutile

Arms
Supporter
-
Joined
Location
hemel hempstead
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Meter tails no rcd in stud wall
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
37
Unsolved
--

Advert

Thread statistics

Created
newfutile,
Last reply from
westward10,
Replies
37
Views
7,813

Advert

Back
Top