Meter tails upgrade for assessment

Discuss Meter tails upgrade for assessment in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

s.keech

I will registering with elecsa soon and going to change c.u in my flat for assessment. Line conductor is 10mm,Earthing conductor is 10mm and bonding conductor is 6mm . I don't know cut out fuse size as it is sealed. The c.u. only has 6 circuits. O.S.G says these are minimum required. Do I need to upgrade to 25,16 or 10 or can I leave it as is or does it depend on size of cut out fuse.Thanks
 
16mm tails for up to 80A DNO fuse. 25mm if 100A.
 