Hi everyone, I'm new to the industry(Qualified a few months ago). I have a client with 6 LED light fixtures on the same circuit/breaker, 3 are working fine and 3 seem to have a neutral fault(230v live to earth,+/-90v neutral to earth and +/-130v live to neutral).
The rest of the installation seems fine(no tripping).
I was just wondering if there is a simple way to locate the fault.
 
That's the most important clue with this fault.

Where are you testing to get the unusal voltages, at the fixture or the Consumer unit?

"3 are working fine and 3 seem to have a neutral fault(230v live to earth,+/-90v neutral to earth and +/-130v live to neutral)"

Seems as though they've tested voltage at each fitting. I wonder if they've looked for loss of neutral at loop out of #3 or into #4.

I'd be amazed if homeowner isn't responsible for this fault, by either pulling neutral out when changing lamps or re-terminating on its sheath.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Centurion
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
South Africa
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Chastech

Thread Information

Title
Neutral fault with LED light fixtures
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Chastech,
Last reply from
nicebutdim,
Replies
3
Views
2,392

Advert

Back
Top