Went for an ECR check and found no earth on lighting circuit, board just been updated last year (Wylex 10 way RCD board), phoned the landlord and said someone recommended to put class 2 fitings but walls have metal capping and switches and accessories are brass/ metal fittings but the code is c2,

Am I right or wrong?, I’m confused
 
Last edited by a moderator:
Went for an ECR check and found no earth on lighting circuit, board just been updated last year (Wylex 10 way RCD board), phoned the landlord and said someone recommended to put class 2 fitings but walls have metal capping and switches and accessories are brass/ metal fittings but the code is c2,

Am I right or wrong?, I’m confused
C2 for me too. It can be changed to a C3 by changing all installed equipment to plastic/class2. Detailed info on this in Best Practice Guide 1. Metal capping (I assume you mean the stuff installed over the cable as protection prior to plasterering?) not relevant to this non-compliance as it isn't usually intentionally earthed.
 
In a perfect world you would rewire the property and advise to do the rewire.

C2 is all you can recommend and a notice at the board to state the CPC is not present to lighting circuit.
with reference to no metal fittings can be connected to that circuit.

Remember you are there to test as the edition it was wired at.
 
In a perfect world you would rewire the property and advise to do the rewire.

C2 is all you can recommend and a notice at the board to state the CPC is not present to lighting circuit.
with reference to no metal fittings can be connected to that circuit.

Remember you are there to test as the edition it was wired at.
You are definitely NOT there to test to the edition it was installed to.
You inspect and test to the current edition of the wiring regulations.
I cannot understand the difficulty in electricians undertaking EICR’s understanding this basic requirement.
 
You are definitely NOT there to test to the edition it was installed to.
You inspect and test to the current edition of the wiring regulations.
I cannot understand the difficulty in electricians undertaking EICR’s understanding this basic requirement.
If the building was built in 16th edition you can not test it to the 18th edition. You can advise to the new editions rules to what applies today.
 
If the building was built in 16th edition you can not test it to the 18th edition. You can advise to the new editions rules to what applies today.
That is incorrect, tell me, as anything we code can be backed up by a regulation, what regulation number would you refer to if for example , sockets upto 32 amps non rcd protected supplying mobile equipment outdoors?
The answer is that you cannot as the 16th edition did not require rcd protection for socket outlets upto the 32 amps ( though it was required for sockets upto 20 amps maybe I can’t remember what rating it stopped at) we have today and unless you actually have a copy of the 16th edition, you cannot reference a regulation number.
 
If the building was built in 16th edition you can not test it to the 18th edition. You can advise to the new editions rules to what applies today.
You test the install as is, AND REPORT any discrepancies to the current regulations, recommending ANY works that are needed to bring the install up to the current standards
 
This subject has been done to death and it winds me right up that supposedly competent and skilled persons are supposed to carry out this type of work, yet they don’t understand the basic requirement to inspect and use the current edition of the wiring regulations as a tool to recommend improvement of safety with the C3 code for example for installations that do not comply with the current edition of bs7671 but are not necessarily unsafe by being installed to a previous standard and do not require upgrading.
 
Therefore you have advised the client with the new code a problem that could occur in the property.

But does not require a rewire maybe a update to a breaker if it does not make the property more or less dangerous.
 
If the building was built in 16th edition you can not test it to the 18th edition. You can advise to the new editions rules to what applies today.
Strictly speaking the testing is little different to previous Regulations however your inspection must include any non-compliance with the requirements of BS7671 which may give rise to danger, see Regulation 653.2. BS7671 will be the current version as previous editions are no longer current therefore departures which may give rise to danger regardless of when it was installed must be noted in the Report.
 
This subject has been done to death and it winds me right up that supposedly competent and skilled persons are supposed to carry out this type of work, yet they don’t understand the basic requirement to inspect and use the current edition of the wiring regulations as a tool to recommend improvement of safety with the C3 code for example for installations that do not comply with the current edition of bs7671 but are not necessarily unsafe by being installed to a previous standard and do not require upgrading.
Or a c2 just like this very thread
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Batley
Business Name
A one Electrical

Thread Information

Title
No earth on lighting circuit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
34
Unsolved
--

Advert

Thread statistics

Created
Mohammed karani,
Last reply from
Midwest,
Replies
34
Views
10,181

Advert

Back
Top