Hi
I wanted to ask peoples opinion on a particular scenario,
Scenario 1
200A Supply into a busbar chamber, this supplies numerous distribution boards but someone has wired a 6mm cable into the busbar which feeds a 20A fused isolator, so potentially you could only draw 20A through the 6mm
Scenario 2
Similarly 100A supply with a 16mm cable which supplies a 63A fused isolator, so the maximum draw is 63A
Scenario 3
32A BS60898 with a 2.5mm cable supplying 1 x switched fused spur, maximum draw is the BS1361 fuse in the spur
Would you have anything wrong with any of the above?
Divided opinions between on our firm
SY is a screened control/power cable and it been sold by the wholesalers as a rough service flex which it definately is not, the outer clear sheath does not possess the durability for the enviroments that its been repeatedly put into, its not suitable for outdoors either as its not UV resistant. Many use it as a power flex for 1ph and 3ph extensions where its under constant reeling and unreeling.. the screening and clear sheath suffer and breakdown when this is done and often the screening is not earthed leaving a potential death-trap waiting to happen.. I remove all such cables I see out of service and over the years have found 2 laid across the floor with live braiding because of metal pins or shards had pierced the cable..
Wholesalers are not competent Electricians and it not their job to tell you the limitations of the cable.. its your job to find out before you ever use such a cable.
We are going off topic here but because the OP's is involved in this conversation I'll let him take it back on topic when he feels the need to.
I don't see anything wrong with using sy in certain situations. If the conductors are adequate to carry the current, if the braid is earthed, if the cpc is one of the cores and not the braid itself, if it is installed indoors or away from UV Rays. The braid can just offer a little more protection rather than using T&E , so for some commercial installations it is fine.
The braid does not offer mechanical protection, NYYJ type cable or H07-RNF if flex is required offer far better mechanical protection
The only advantage with SY is the increased emc shielding which is required in control circuits etc
From what Ive read I agree:
Welcome to Doncaster Cables - SY Steel Wire Braid Armoured Flexible PVC Control Cable
This cable is also used by electricians in certain fixed installations where only light mechanical stress may occur. This cable can also be used outdoors (but should be protected); however, it is best suited to dry or moist conditions indoors.
My view
Scenario 1 - 6mm cable from busbar feeding 20A isolator is fine for a short run - 3m
Scenario 2 - I would prefer to see the cable capable of carrying the supply current regardless if the load is limited, especially over any distance
Scenario 3 - I wouldnt do it I think its completely wrong, 2.5mm in a C32A BS60898 over 3m distance
2 key points ...fixed installation and outdoor use should be protected ..i.e. run in a pipe etc to shield it from the UV
My view
Yes agree
Many of my industrial installs rely on the ommitance for overload protection due to the nature of the load been fixed, this can safe alot of material costs but care needs to be taken that Zs values are still met.
It would probably fail Zs with any large distance and this is the reason why you can't but it could be done over 5m if load is fixed or limited using O/L protection ommitance regulations
It is situation dependent but even variable loads that have a FLC that acts as a limiting factor can be classed as fixed loads but as always a good knowledge of these design methods is essential as a slight error in the design stages can be costly when you find you fail Zs compliance.
Preferred Method
fattony,
Darkwood,