Have just completed a consumer unit change, Ze is reading at 0.09, PFC reading at 9.5kA, Its on a TN-CS System and about 150m from nearest transformer. I am not highly experienced in Testing, and unable to establish what is going on, but I am suspecting there is a big problem! I am using a Megger MFT1553, which is also tripping internally (as in displaying 'trp on the tester) when trying to carry out Zs tests across all circuits using the 'no trip' function. Any ideas??? :confused:
 
I have also tested the circuits using my Megger LT320 and it is displaying 'CHK'
Also have taken both Meggers to another house to eliminate equipment failure and both are functioning correctly.

I am panicking as the job is for my first ELECSA inspection next week!!! HELP!! :eek:

Im hoping its just my lack of experience missing something very simple!
 
When using the no trip function all 3 leads must be used. Make sure you have a good connection on all 3 for the full duration of the test. Can't see the Ze reading being of any relevance. Are all your R1 + R2 readings ok?
 
Have just completed a consumer unit change, Ze is reading at 0.09, PFC reading at 9.5kA, Its on a TN-CS System and about 150m from nearest transformer. I am not highly experienced in Testing, and unable to establish what is going on, but I am suspecting there is a big problem! I am using a Megger MFT1553, which is also tripping internally (as in displaying 'trp on the tester) when trying to carry out Zs tests across all circuits using the 'no trip' function. Any ideas??? :confused:

Hi mate,

I've got the same meter(1552) - the only time I've ever had this message was when I (foolishly) forgot that the no-trip loop test was a three lead test:o

I'd been trying to test with the two leads and it came up 'trp' each time.
 
I concur.

This is from the 1553 instruction manual.

Page10.jpg
 
Thanks for the replies, I have managed to get a Zs reading on my ring mains (using the 'plug' test lead) Im not sure why is it giving me a reading now, as before it was just stating 'trp' on the tester and not knocking out the RCD's. however, I have tried using the 3 lead method on my lighting circuits, as above, but it is knocking the RCD's out now! (I have been able to obtain a reading on my cooker radial using the 3 lead method though) Hmmmmm.....
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Problems with Zs (and possibly Ze and PFC) Using Megger MFT1553 Tester
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
AMC,
Last reply from
AMC,
Replies
6
Views
9,906

Advert

Back
Top