Discuss RCBO fly leads in the UK Electrical Forum area at ElectriciansForums.net
somersetsparks
Heres a debate for you, seeing as this place is as dead as a doornail today.
I have been testing a street of domestic properties recently, wired in 2008 with all rcbo's. In some properties the electrician has put all the white fly-leads into one terminal in the earth bar, In the others they have put each one in with the respective circuits cpc.
Which way do you do it?
I'll start the ball rolling by saying I would put them all into the same terminal (for domestic anyways) for the following reasons
a) When you come to doing an EICR, you only have to undo one connection to test the circuits using method 2 rather then disturb every single earth connection.
b) its a lot bl***y easier to install.
When it comes to commercial where there may be only 1 or 2 rcbo's in a TPN board then I would put them with their respective cpc.
Opinions?
As a side question: do you sleeve the white flylead in green/yellow? Most I've seen (admittedly not thousands) are sleeved, but according to the 'official' colours, cream is the colour of 'functional earth' not G/Y.
Don't sleeve them, They would be green/yellow if they were meant to be, as you rightly say, cream is the colour for a functional earth.
both in same terminal.
if your CU has the facility to provide 2 earth terminals for each circuit , then i would reserve the use of the second terminal for high integrity earthed circuits that require a seperate connection for both protective conductors.
if your CU has the facility to provide 2 earth terminals for each circuit , then i would reserve the use of the second terminal for high integrity earthed circuits that require a seperate connection for each protective conductor.
I used to always do it that way biff but after testing a lot of houses, it makes it a right B***ard to megger, you have to disturb the cpc of every circuit to remove the flylead. From now on I am putting all the cream coloured leads into a group and into one terminal of the earth bar as it makes doing insulation resistance an easy job.
Either way its completely inconsequential, i'm just debating for the sake of it really
I like the term 'bungled', makes me sound like a right bodging *** lol. I just think it makes sense when thinking of future EICR's on properites although it may sound a bit rough
Doesn't really matter does it - can and is done either way.
Just over time and with several other electricians in things get tangled ... if everything seperate, should you ever have to replace the RCBO then it is usually easier to figure out which fly-lead is which when they're seperate.
That's the only reason i try put them in there corresponding earth terminals.
I always strip approx 100mm of the insulation off the fly lead and then obviously twist it together nice and tight with the cpc......as it should be done!!!!! :)
Seriously though I usually put fly lead with the respective cpc
twisting tri-rate with solid cores or stranded ?
cough* bodge *cough
I put them in with the circuit CPC....
But thats because most of the DBs I work on will just have a few in rather that a full DB as in a domestic...
Does make sense to put them all in bar, never seen it done...
Reply to RCBO fly leads in the UK Electrical Forum area at ElectriciansForums.net
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking...
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Hi All Seen this on a few jobs now where they have on the Downlight fittings where the CPC is terminated outside the enclosure of the Downlight...
5K
Hi, I've bought a "yagusmart" smart switch from Amazon and it has no earth terminal. Although there are no metal facing parts I would think the...
