Hi all,

I have been to a property where the tails come out of the meter and into an RCCB which then feeds the main switch of the consumer unit. All circuits are protected by MCBs.

If I'm adding a new circuit, is it best put in an RCBO instead of an MCB?

Thanks
 
Hi Noob,

A new circuit would need notifying under Part P of the building regs. As your profile shows that you're an apprentice you could maybe undertake this job with one of the electricians that you work with.

Also, if you don't already have it, get yourself access to the trainees forum.

Good advice
 
Reg number please?

531.2.5 - An RCD shall be so selected and the electrical circuits so subdivided that any protective conductor current which may be expected to occur during normal operation of the connected load(s) will be unlikely to cause unnecessary tripping of the device.

And:

314.1 - Every installation shall be divided into circuits, as necessary, to:

(i) avoid danger and minimise inconvenience in the event of a fault
(ii) facilitate safe inspection, testing and maintenance (see also Section 537)
(iii) take account of hazards that may arise from the failure or a single circuit such as a lighting circuit
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor (PE) currents not due to a fault
(v) mitigate the effects of electromagnetic disturbances (see also chapter 44)
(vi) prevent the indirect energising of a circuit intended to be isolated.
 
531.2.5 - An RCD shall be so selected and the electrical circuits so subdivided that any protective conductor current which may be expected to occur during normal operation of the connected load(s) will be unlikely to cause unnecessary tripping of the device.

And:

314.1 - Every installation shall be divided into circuits, as necessary, to:

(i) avoid danger and minimise inconvenience in the event of a fault
(ii) facilitate safe inspection, testing and maintenance (see also Section 537)
(iii) take account of hazards that may arise from the failure or a single circuit such as a lighting circuit
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor (PE) currents not due to a fault
(v) mitigate the effects of electromagnetic disturbances (see also chapter 44)
(vi) prevent the indirect energising of a circuit intended to be isolated.

Not fault current.
the second one basically just means don't put everything on one circuit.
 
UKESrail

I think the point being made is that these Regs youve found are all admirable but they are not retrospective! The point has already been made (the analogy with a car from the past for example, without ABS).

when you quote for a job you do not have to "fix everything".

As a further example, if you fit a plastic CU today, and it turns out from the new amendment onwards all CUs need to be steel, are you then going to go back and insist they change the one you fitted a few months back?

Catch my drift?

not sure if you are on the wind up.......
 
UKESrail

I think the point being made is that these Regs youve found are all admirable but they are not retrospective! The point has already been made (the analogy with a car from the past for example, without ABS).


when you quote for a job you do not have to "fix everything".

As a further example, if you fit a plastic CU today, and it turns out from the new amendment onwards all CUs need to be steel, are you then going to go back and insist they change the one you fitted a few months back?

Catch my drift?

not sure if you are on the wind up.......

Not at all.

1) The guy asked simply for the reg which I have stated.

2) My issue with the regs not being retrospective (which I fully accept is the case) is that you will need to know exactly (1) when that specific reg came into force. and (2) when the installation and subsequent alterations were carried out.

The first of these is not impossible to find out but would take days to verify beyond doubt and the 2nd will be impossible to state and would be a guess at best. The car example you gave does not work in reality because the V5 document will always have a date on. An electrical installation without all the certificates and reports made available is anyone's guess.

I do not like to work on guess' and would rather be 100% sure that I am doing the right thing. I know there is interpretation in this but this is my humble opinion.
 
Not at all.

1) The guy asked simply for the reg which I have stated.

2) My issue with the regs not being retrospective (which I fully accept is the case) is that you will need to know exactly (1) when that specific reg came into force. and (2) when the installation and subsequent alterations were carried out.

The first of these is not impossible to find out but would take days to verify beyond doubt and the 2nd will be impossible to state and would be a guess at best. The car example you gave does not work in reality because the V5 document will always have a date on. An electrical installation without all the certificates and reports made available is anyone's guess.

I do not like to work on guess' and would rather be 100% sure that I am doing the right thing. I know there is interpretation in this but this is my humble opinion.

Also I would add that many lesser sparks installed 'front end' RCDs when the 17th Edition came out in an attempt to afford the installation adequate protection. So it is not unreasonable to suggest that some 'front end' RCDs have been fitted recently.
 
(i) avoid danger and minimise inconvenience in the event of a fault

This one is as clear as a bell.

Not at desk at mo so no books, but how do you explain the picture near the front of your OSG regarding TT installs with a single RCD upfront? Or do you think the IET have made a mistake?
 
But did you not say that's not allowed? No single RCD ?

I did as a generalisation on a Sunday without my book. I did say that I would quote the specific reg. Plus TT systems have always been like this so did not feel at the time required specific mentioning. Installing a non time delayed RCD would not meet the regs quoted. A time delayed would.
 
But did you not say that's not allowed? No single RCD ?
& TT installs don't have to have a 100mA time delay RCD.

You would not meet this reg if you put a 30mA non time delayed RCD at the origin of a TT installation.

I have not got every version of BS7671 printed to check when this reg came into force. Which is kind of my point.
 
(i) avoid danger and minimise inconvenience in the event of a fault

This one is as clear as a bell.

That reg was already present even in the 16th edition, but was interpreted by a lot of sparks to mean only the OCPDs and final circuit arrangement, hence we had lot of upfront 30mA RCDs fitted to 16th Edition installs, the introduction of the 17th where RCD everything in domestic became the new fad, the rule was clarified further and implicitly applied to RCDs hence the so called dual RCD 17th edition boards, which itself was a 'kludge'
 

Reply to RCCB as main switch? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
667
Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
519

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses