Hi all,
I have been to a property where the tails come out of the meter and into an RCCB which then feeds the main switch of the consumer unit. All circuits are protected by MCBs.
If I'm adding a new circuit, is it best put in an RCBO instead of an MCB?
Hi Noob,
A new circuit would need notifying under Part P of the building regs. As your profile shows that you're an apprentice you could maybe undertake this job with one of the electricians that you work with.
Also, if you don't already have it, get yourself access to the trainees forum.
Good advice
Reg number please?
531.2.5 - An RCD shall be so selected and the electrical circuits so subdivided that any protective conductor current which may be expected to occur during normal operation of the connected load(s) will be unlikely to cause unnecessary tripping of the device.
And:
314.1 - Every installation shall be divided into circuits, as necessary, to:
(i) avoid danger and minimise inconvenience in the event of a fault
(ii) facilitate safe inspection, testing and maintenance (see also Section 537)
(iii) take account of hazards that may arise from the failure or a single circuit such as a lighting circuit
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor (PE) currents not due to a fault
(v) mitigate the effects of electromagnetic disturbances (see also chapter 44)
(vi) prevent the indirect energising of a circuit intended to be isolated.
And:
Not fault current.
the second one basically just means don't put everything on one circuit.
UKESrail
I think the point being made is that these Regs youve found are all admirable but they are not retrospective! The point has already been made (the analogy with a car from the past for example, without ABS).
when you quote for a job you do not have to "fix everything".
As a further example, if you fit a plastic CU today, and it turns out from the new amendment onwards all CUs need to be steel, are you then going to go back and insist they change the one you fitted a few months back?
Catch my drift?
not sure if you are on the wind up.......
UKESrail
Catch my drift?
Not at all.
1) The guy asked simply for the reg which I have stated.
2) My issue with the regs not being retrospective (which I fully accept is the case) is that you will need to know exactly (1) when that specific reg came into force. and (2) when the installation and subsequent alterations were carried out.
The first of these is not impossible to find out but would take days to verify beyond doubt and the 2nd will be impossible to state and would be a guess at best. The car example you gave does not work in reality because the V5 document will always have a date on. An electrical installation without all the certificates and reports made available is anyone's guess.
I do not like to work on guess' and would rather be 100% sure that I am doing the right thing. I know there is interpretation in this but this is my humble opinion.
Not at all.
Also I would add that many lesser sparks installed 'front end' RCDs when the 17th Edition came out in an attempt to afford the installation adequate protection. So it is not unreasonable to suggest that some 'front end' RCDs have been fitted recently.
But did you not say that's not allowed? No single RCD ?
I did as a generalisation on a Sunday without my book. I did say that I would quote the specific reg. Plus TT systems have always been like this so did not feel at the time required specific mentioning. Installing a non time delayed RCD would not meet the regs quoted. A time delayed would.
& TT installs don't have to have a 100mA time delay RCD.
You would not meet this reg if you put a 30mA non time delayed RCD at the origin of a TT installation.
I have not got every version of BS7671 printed to check when this reg came into force. Which is kind of my point.
This one is as clear as a bell.
That reg was already present even in the 16th edition, but was interpreted by a lot of sparks to mean only the OCPDs and final circuit arrangement, hence we had lot of upfront 30mA RCDs fitted to 16th Edition installs, the introduction of the 17th where RCD everything in domestic became the new fad, the rule was clarified further and implicitly applied to RCDs hence the so called dual RCD 17th edition boards, which itself was a 'kludge'
Agreed and interoperated incorrectly in my view. I think the reg is crystal clear and mentions nothing about RCDs or OCPDs.
It wasn't stated so crystal clear in the 16th though, and like a lot of regs was open to interpretation, the RCD parts of that edition being almost an "afterthought" at least in the earlier 16th editions (pre amds), the 17th clarified it further.
And:
As usual BS 7671 gobbledegook
Yes I'm well aware of the regs - but in this instance we are debating the way to add a circuit to an existing install, not a new CU and not a rewire.
You do not apply BS 7671 retrospectively
BS 7671 is not statute.
So I view people like you with the "its illegal", "its unsafe", as rip off merchants at best, cowboys at worst.
No it isn't, but that is what we work to along with some other regulations. It is also what will be referred to by others and you will have to justify why you worked outside it. I find it easier to work within it. That is also unfair to label UKES a rip off merchant for offering to carry out work to current regulations, the customer does not have to accept it so they.
With respect you have no idea who I am mate. Best leave it like that. Ok?
I disagree. IF and I say IF the installation has bonding and a 30mA RCD then why would a new CU be needed? Sure offer the client 2 choices but saying it HAS to be changed is a misrepresentation of the regs.
Just saying.