Currently reading:
RCCB as main switch?
Discuss RCCB as main switch? in the UK Electrical Forum area at ElectriciansForums.net
N
Noob2013
Hi all,
I have been to a property where the tails come out of the meter and into an RCCB which then feeds the main switch of the consumer unit. All circuits are protected by MCBs.
If I'm adding a new circuit, is it best put in an RCBO instead of an MCB?
But did you not say that's not allowed? No single RCD ?
I did as a generalisation on a Sunday without my book. I did say that I would quote the specific reg. Plus TT systems have always been like this so did not feel at the time required specific mentioning. Installing a non time delayed RCD would not meet the regs quoted. A time delayed would.
& TT installs don't have to have a 100mA time delay RCD.
You would not meet this reg if you put a 30mA non time delayed RCD at the origin of a TT installation.
I have not got every version of BS7671 printed to check when this reg came into force. Which is kind of my point.
(i) avoid danger and minimise inconvenience in the event of a fault
This one is as clear as a bell.
That reg was already present even in the 16th edition, but was interpreted by a lot of sparks to mean only the OCPDs and final circuit arrangement, hence we had lot of upfront 30mA RCDs fitted to 16th Edition installs, the introduction of the 17th where RCD everything in domestic became the new fad, the rule was clarified further and implicitly applied to RCDs hence the so called dual RCD 17th edition boards, which itself was a 'kludge'
Agreed and interoperated incorrectly in my view. I think the reg is crystal clear and mentions nothing about RCDs or OCPDs.
It wasn't stated so crystal clear in the 16th though, and like a lot of regs was open to interpretation, the RCD parts of that edition being almost an "afterthought" at least in the earlier 16th editions (pre amds), the 17th clarified it further.
531.2.5 - An RCD shall be so selected and the electrical circuits so subdivided that any protective conductor current which may be expected to occur during normal operation of the connected load(s) will be unlikely to cause unnecessary tripping of the device.
And:
314.1 - Every installation shall be divided into circuits, as necessary, to:
(ii) facilitate safe inspection, testing and maintenance (see also Section 537)
(iii) take account of hazards that may arise from the failure or a single circuit such as a lighting circuit
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor (PE) currents not due to a fault
(v) mitigate the effects of electromagnetic disturbances (see also chapter 44)
(vi) prevent the indirect energising of a circuit intended to be isolated.
As usual BS 7671 gobbledegook
Yes I'm well aware of the regs - but in this instance we are debating the way to add a circuit to an existing install, not a new CU and not a rewire.
You do not apply BS 7671 retrospectively
BS 7671 is not statute.
So I view people like you with the "its illegal", "its unsafe", as rip off merchants at best, cowboys at worst.
No it isn't, but that is what we work to along with some other regulations. It is also what will be referred to by others and you will have to justify why you worked outside it. I find it easier to work within it. That is also unfair to label UKES a rip off merchant for offering to carry out work to current regulations, the customer does not have to accept it so they.
With respect you have no idea who I am mate. Best leave it like that. Ok?
I disagree. IF and I say IF the installation has bonding and a 30mA RCD then why would a new CU be needed? Sure offer the client 2 choices but saying it HAS to be changed is a misrepresentation of the regs.
Just saying.
Reply to RCCB as main switch? in the UK Electrical Forum area at ElectriciansForums.net