RCD test - 2 RCD's in sequence

Discuss RCD test - 2 RCD's in sequence in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

DoBBY

I have a garage install protected by a 30mA rcd and a 32A breaker at main DB in dwelling, I then have a new CU in garage which also has a 30mA rcd protecting sockets and lights.

When I do the RCD test I am getting bad results. When I do the 1 x the RCD in the garage CU is not tripping but the RCD at the original DB is...what the hell is going on..?

I can't put the circuit on the main switch side of the DB because there is no room so it has to stay on the RCD side....

Any ideas?
 
as said running two rcd is pointless and the most sensitive will trip first, either remove the rcd from garage or move the circuit to a unprotected way in house (depending on wether the distribution cable requires rcd protection)
 
Did you not read my last post, to your other question ?. check it out it explains all you have to do.
your last post about EIC forms
 
Last edited by a moderator:

Reply to RCD test - 2 RCD's in sequence in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock