hi everyone. new to this. just carrying out a pir on a pub, and when looking at the d/b wiring, the neutrals/cpc etc dont marry up to the breakers. on the pir can i just limit doing a ring final test and code it or will have to persevere and find the right cables. as its a pub up and running i cant just disconnect cpc's etc. thanks for any comments
 
Note it on the cert that neutrals in the DB cannot be matched to the corresponding mcb's for testing purposes...(code 4). Carry out end to end tests at a socket outlet on the ring,not strictly correct but the results will be the same.
 
Note it on the cert that neutrals in the DB cannot be matched to the corresponding mcb's for testing purposes...(code 4). Carry out end to end tests at a socket outlet on the ring,not strictly correct but the results will be the same.

Personally I would opt for a recommendation code 2 if they can't be identified.
 