trying to find answers in the reg book, but is there anything to say you can't install say a larger ring circuit for a sub main? to reduce volt drop / cable size etc.

Normally you would obviously install a large enough cable, but would this be acceptable , whats our thoughts?
 
trying to find answers in the reg book, but is there anything to say you can't install say a larger ring circuit for a sub main? to reduce volt drop / cable size etc.

Normally you would obviously install a large enough cable, but would this be acceptable , whats our thoughts?
Surely it would then be a parallel circuit/parallel conductors .....There are requirments for installing/designing a parallel circuit/conductors.

A brief guide to the use of parallel conductors - https://www.voltimum.co.uk/articles/brief-guide-use-parallel-conductors
 
Yes, seen plenty sub-mains cables ran in parallel. Ie it’s eaiser to install / terminate 2 x 150mm SWAs, than one big beast of 300mm2!
Only ring circuit (for sub-main) I’ve seen was in a prison, a 4 or 6mm2 ring circuit in trunking, ran round a number of cells, each had a small DB (fitted out side above the door) for the light and socket.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
north yorkshire

Thread Information

Title
ring circuit for a submain?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
vde-electrician,
Last reply from
ChrisElectrical88,
Replies
8
Views
2,709

Advert

Back
Top