Search the forum,
Discuss shower priority unit positioning in the UK Electrical Forum area at ElectriciansForums.net
hi everyone, I'm in the process of converting an outbuilding into a granny annex which will have an electric shower installed I've been told I'll need a shower priority unit positioned in the main house next to the cu which will then feed the annex shower directly without need to involve the cu in the annex, what armoured cable will I need to supply both the annex cu for all the other circuits and shower independently , thanks
Why do you need a priority unit? Have you looked at other hot water solutions instead of electric showers?
As far as cable size and type goes you haven't given us anywhere near enough information to even give a rough estimate.
We need to know information such as what the electrical load will be on each circuit, circuit length, nature of the route, how it will be installed.
We would also need to know what type of incoming supply you have, what the earthing system is and what the earth fault loop impedance/prospective fault currents are.
The point of a priority unit is so that you can't use 2 showers at the same time, and one of them will have a priority over the other (Basically a contactor).
Being told you need one is suggesting that you may not have the capacity.
More info would be helpful.
I'm doing most of the work myself including putting in an armoured 16mm cable which is about a 30 m run and will get everything signed off when completed i understand why I need the priority unit , there's 9kw shower going in the annex and the main fuse won't support 2 showers, my question is can I run an 16mm 5 core cable to supply both shower directly and annex cu, the other circuits at lights 6amp sockets 32amp cooker 32amp smoke alarm 6amp
I was told that would be the way to go
I've no idea about the installation conditions, but 16mm seemed unusual for the stated load. There may be valid reasons for using this size, but none that immediately jump out at me.
The use of 5 core cable for 2 circuits isn't particularly unusual, provided ADS is satisfied.
You really need to be speaking to the electrician who will be testing and signing it off. Otherwise you risk doing the work and then it not getting signed off and certified.
do you think 10mm would work?
Have you actually found out how you will get this additional work 'signed off'. It sounds like this is part of some building work, that may be under planning or a building notice? Have you spoken to your LBC about this?
If the main fuse won't support 2 showers will it support 1 shower and 2 cookers?
Whilst a single multicore cable can be used for multiple circuits this would usually only be done when those circuits are terminating in the same place. In this case you would need to joint the 5 core cable onto 2 other cable, one to go to the CU and one to go to the shower, this just adds an unnecessary and ugly joint to the installation.
Also why would you use 5 core SWA for 2 circuits?
He could take the 5 core to one CU and feed the shower from there.
Reply to shower priority unit positioning in the UK Electrical Forum area at ElectriciansForums.net
