SpannerSpark

I havent come across this before, wondered if its common and what it signifies in the ring.
Remeasured 3 times and got within 20mohms or so each time so pretty sure its not a zeroing the meter thing.
2.5:1.5 TW/E ring. I went around all of downstairs rooms, did min of few sockets in each room nice even results all the way around. Just not 1/4 of r1, r2 etc

r1=1.15
r2=1.82
rn=1.13

R1+Rn =0.57 (approx half)
R1+R2=0.78 (only a little bit less than half)

Any ideas?
PS Job was to move a socket and add a couple more.
Install is in <10 year old house, doesnt look to have been messed about much apart from has had an extension added in the last few years.
 
comes out in my head as 0.263 as opposed to 0.25. not far out. IMO.
 
They look fine to me as well.
Remember measurement/contact errors.
I wouldn't worry about a few 100ths of Ohms!
It's Friday, go and enjoy yourself.
 
Correct me if Im missing something hugely obvious here but based on your r1/r2/rn readings you should be looking at getting around R1+R2 = 0.74 and R1+Rn = 0.57

You actually get 0.78 & 0.57? ---- whats the issue? They are pretty good results especially if constant around the sockets!
 
case of overthinking, methinks. as archie says, it's friday, it's beer o'clock, move on.
 
nah..... 0.25 is 1/4 as in R1+R2 = (r1+r2)/4. humpff.
 
Thanks guys. I havent done any testing for a good while and just got a mental block that I should be expecting R1+R2 to be 1/4 of r1 or r2, rather than r1+r2. When i think about it i am being a bell-end.
 
we all make mistakes, as the hedgehog said, climbing off the back of the bog-brush.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Socket ring readings. R1+R2 approx half r1, r2
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
SpannerSpark,
Last reply from
telectrix,
Replies
13
Views
2,514

Advert

Back
Top