pic 3 dangerous code C1. no excuse for the sake of a couple of bob for blanks.
 
And no blanking plates in CU, nor protection on 2.5mm cable down wall, nor protection on cable to consumer unit. Shoddy work shows a careless worker. I have not looked further under floors and in loft. Some of the places are now inaccessible. If I had been 20years younger I would have found him and taken him to task very strongly by using my East end upbringing.
 
And no blanking plates in CU, nor protection on 2.5mm cable down wall, nor protection on cable to consumer unit. Shoddy work shows a careless worker. I have not looked further under floors and in loft. Some of the places are now inaccessible. If I had been 20years younger I would have found him and taken him to task very strongly by using my East end upbringing.

So was he a scam member? did he leave a cert? have you seen it?
 
Probably a scam member. He issued an ICM4 'certificate'. Does that mean he is not a member of NICIEC. He did say he was qualified to test other installations. I don't fully understand the qualification and NICIEC membership requirements. I thought all electricians had to be a member. Just like Gas Safe for gas work.
 
Probably a scam member. He issued an ICM4 'certificate'. Does that mean he is not a member of NICIEC. He did say he was qualified to test other installations. I don't fully understand the qualification and NICIEC membership requirements. I thought all electricians had to be a member. Just like Gas Safe for gas work.

no you don't have to. you can simply contact building control to certify your work for a fee.

a lot of firms join a scam because its a lot cheaper and more convenient
 
pic 3 dangerous code C1. no excuse for the sake of a couple of bob for blanks.
and not just this lack of understanding on new install either....
like i said the other day had a look at a report on an install in leeds that someone had carried out....
amongst other rubbish and falseties he`d given missing blanks a 3.....
 
Sadly the NICEIC's (and the others) argument about checking work (the 'driving' scenario) falls over because it assumes a base level of competence to start with. If you have been driving for 20/30/60 years it is reasonable to assume (yes, there will be exceptions, I know) that when behind the wheel you know what you are doing. It is not the same for an 18yr old just passed his test, and this is reflected in his insurance premiums.

Therefore, the analogy only actually works if the least qualified and shortest period served (which, for arguments sake we'll call a Electrical Trainee) are more closely supervised than someone who did all his quals and has continuously served for the last 20+ years. The latter then yes you CAN just inspect once a year, but the former I'd be wanting to have the inspector drop round at least every five notifications 'when next passing'. All it would take is five minutes to do a visual.
 
On a technical note, where have 4-5 of the bl00dy neutrals gone to in the DB piccy. Looks to be approx 12-13 lives and only 8 blues.... puzzled...

Just looked again...think camera angle and the mess of cables have tricked me!
 
Dear Forum - I have only just come across this forum thanks to someone sending a PM message.

I can assure you NICEIC takes very seriously any complaint made against one of our contractors. If the customer makes a complaint direct we will carry out a full investigation, send out an engineer to do an inspection and, if required, order the contractor to rectify the work to the required standard.

No complaint has been made on this occasion from the customer but if Zeddess would like to PM me the details of the contractor he/she believes carried out the work we can carry out an investigation and speak to the contractor direct if they are found to be at fault.

NICEIC operates the most robust and rigorous qualification for registration requirements in the UK. This includes, but is not limited to, an inspection of a representative sample of the companies work, assessment at their premises to ensure they have documentation and records, employs only competent persons to carry out electrical work, has evidence of required insurances and an, inspection of their equipment and premises. Most importantly, it includes a requirement for regular periodic inspections and assessments of organisations and principle named individuals to ensure standards are continually met.

However, in the same way that theDVLA cannot oversee every journey carried out by those with a driving licence, the NICEIC is not in a position to test every electrical installation itself. The fact that a contractor has been approved to work to best industry standards on assessment cannot, regrettably, rule out the possibility that a contractor, or someone working for them, may be negligent in relation to a specific electrical installation in the future. just as drivers have a duty of care to respect the rules of the road at all times, so do electricians assessed by NICEIC.

If a contractor is found to be guilty of not keeping within the rules and regulations for enrolement, they will be de-registered immediately. Last year we de-registered 518 contractors who failed to meet the strict requirements of enrolment .

I hope this answers some of the forum’s queries and as mentioned will be happy to deal with Zedess’ complaint. I would also urge any other contractors who come across similar incidents to get in touch with NICEIC direct – as we can only act on these issues if we are informed of them. Email [email protected]

Finally, apologies for lack of interaction on the forum lately – NICEIC will endeavor to check and respond, where appropriate, more regularly in the future.
well the entry assessment for any of the schemes is hardly taxing in any way, shape or form is it....after all its not meant to be...is it....

but feels its in a position to instruct folk on max. Ra values etc

 
@ NICEIC ENGINEER.
If this work was carried out by an NIC approved contractor I am appalled that the NIC has allowed a contractor capable of such shoddy standards to be enrolled. I have worked for two NICEIC approved contractors continuously since 1978 and have always believed the NIC enforced rigorous standards. Your answer to this thread is frankly laughable, for all the fine words you are clearly unable to see the truth,that your scheme is not working if cowboys like this carry the NIC flag of 'excellence'.
Where does that leave bona-fida NIC contractors who uphold the standards they believe the NIC represents?......it leaves them tarred with the same brush,the lowest common denominator is always the one they will be associated with.
And as for the myriad Joe public viewing this forum......well they now know that employing an NICEIC contractor gives them no more assurance than employing Bob from down the Pub.
Thanks for that NICEIC....you have destroyed the credibility of a great organisation in your pursuit of profit.
 
@ NICEIC ENGINEER.
If this work was carried out by an NIC approved contractor I am appalled that the NIC has allowed a contractor capable of such shoddy standards to be enrolled. I have worked for two NICEIC approved contractors continuously since 1978 and have always believed the NIC enforced rigorous standards. Your answer to this thread is frankly laughable, for all the fine words you are clearly unable to see the truth,that your scheme is not working if cowboys like this carry the NIC flag of 'excellence'.
Where does that leave bona-fida NIC contractors who uphold the standards they believe the NIC represents?......it leaves them tarred with the same brush,the lowest common denominator is always the one they will be associated with.
And as for the myriad Joe public viewing this forum......well they now know that employing an NICEIC contractor gives them no more assurance than employing Bob from down the Pub.
Thanks for that NICEIC....you have destroyed the credibility of a great organisation in your pursuit of profit.

And why would a trade organisation need to make a profit anyway? Surely it should be cost neutral
 
you mean like this guy did (NIC ENGINEER)...?
all a publicity stunt....they aint interested

and whats this about the chap who did that mountain of shyte `meeting criteria`..?

take a look at the pics man......
does that look like meeting any sort of criteria to you?

Your saying that a register of electricians with a boat load of qualifications hanging out their back pocket would stop this happening, it won't.

He probably has all them. Too many people on here when they see this type of work are quick to jump in and say its the polish lot or the Electrical Trainee brigade when the fact is I see this type of work from time served highly qualified electricians who for whatever reason don't give a ---- anymore.

Don't blame a building regulation and the introduction of schemes for this, nor should you seek it's abolishment to make things right.

This has been going on for years and its only now via the Internet and camera phone technology that people are able to share it with the big bad world.

I didn't say it wasn't bad and I didn't say that the NICEIC are interested. I was making the point that your idea that a register where only the ones with the most quals gets in wont solve it.
 
I should have remembered that. Something about a 'competent person' doing the work. Four years ago I did add new installation in a new loft room for my daughter (new small consumer unit etc.) and established that the Building Control would inspect and issue the Building Regs cert. All this inclusive of the fee for the whole works. At the time they had to be prompted to accept this as there was a lot of confusion in this area. It is their decision whether to pay an Electrical inspector or not. Trying to arrange connection by the Elec supplier was fun as they did not seem very customer oriented. One person would come and disconnect whole supply, your electrician then makes the connection, and then some time later that day they re-connect the supply. I had added Henley blocks.
Last year my next door neighbour was asked by building control for an extra £180 to inspect the one extra light he was fitting in an additional toilet room. Later re-funded by building control as they did not seem to understand what the 'rules' were.
So are we saying that there are still 'cowboys' out there (not NICIEC). Does employing an NICIEC electrician protect the consumer?
 
I should have remembered that. Something about a 'competent person' doing the work. Four years ago I did add new installation in a new loft room for my daughter (new small consumer unit etc.) and established that the Building Control would inspect and issue the Building Regs cert. All this inclusive of the fee for the whole works. At the time they had to be prompted to accept this as there was a lot of confusion in this area. It is their decision whether to pay an Electrical inspector or not. Trying to arrange connection by the Elec supplier was fun as they did not seem very customer oriented. One person would come and disconnect whole supply, your electrician then makes the connection, and then some time later that day they re-connect the supply. I had added Henley blocks.
Last year my next door neighbour was asked by building control for an extra £180 to inspect the one extra light he was fitting in an additional toilet room. Later re-funded by building control as they did not seem to understand what the 'rules' were.
So are we saying that there are still 'cowboys' out there (not NICIEC). Does employing an NICIEC electrician protect the consumer?

It is supposed to. As you can see by the content of this thread though, it is no guarantee, NICEIC or any other scheme.
As you can also see, their response to shoddy work is aloof at best, total apathy at worst.
They let any tom dick and harry in, but won't admit their system is not working.
 
Bottom line, scams, or no scams, there is nothing to stop shoddy work.

If the scams were seen to inspect, intervene and uphold best practice etc, etc, then the slide downhill may stop.
 

Reply to Some pics from a FULL rewire. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock