On a job at the mo. A replacement c/u , rewire shower and some sockets etc.

The c/u is near the kitchen fed by a 16mm t+e sub main. The sub is fed from a switch fuse in the hall way. Prior to the switch fuse is a older 100ma RCD. you know the big grey and black fellas.

My question is should i leave the older RCD in to protect the sub (subject to test). The c/u will have 2 30ma RCD's installed so discrimination will be ok.

Should I remove or leave it if it checks out ok.

Feedback welcome

G
 
There wont be any discrimination between the 100mA RCD and the 2 30mA RCD's in the CU......unless it's a time delayed "S" type one.

Depending on how the sub-main is installed it may need RCD protection of the 30mA variety though.
 
Ok, if the T+E sub is buried in the wall less than 50mm and not in earthed mateallic conduit etc etc then it will need additional protection by 30mA RCD.

If it's surface run in it's entireity though in pvc trunking for instance, then it would not need the additional 30mA protection. If it's a TT system though then it would need an RCD up front regardless of install method i.e a 100A 100mA time delayed type.
 

Reply to Sub main in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top