hi there guy's i have to move a consumer unit from the understair's cupboard,to the larder cupboard,which back's onto the wall,where the original consumer unit sit's,the problem i have is i can't remember the maximum length the 25mm tail's you are allowed to have, without installing a separate i00 amp isolater,cheer's john
 
hi there guy's i have to move a consumer unit from the understair's cupboard,to the larder cupboard,which back's onto the wall,where the original consumer unit sit's,the problem i have is i can't remember the maximum length the 25mm tail's you are allowed to have, without installing a separate i00 amp isolater,cheer's john

Not an isolator, an overcurrent protective device and it's normally 3 Metres depending on the DNO requirements.
 
Last edited:
It's the DNO that reccomend a maximum length of supply tails before an additional switchfuse is needed, the general rule of thumb is 3M if internal and 4M if external.
 

Reply to Supply tails length????? in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock