clanky

~
Aug 16, 2018
59
33
93
Suffolk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician
Business Name
Marine electronics
Hello again,
Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter, which was installed a couple of years ago (outbuildings on the second phase of a split phase supply) has been wired with 16mm tails but with a 100a isolater switch post meter. Should these have been 25mm? The installer (plumber who'd been on a meter course apparently) had no idea what i was going to install downline of this meter so shouldnt have he erred on the safe side?
 
No, the 100A refers to the maximum rating of the switch. Assuming some normalcy here, 16mm tails are rated to 99A so I'd suspect you probably have an 80A incoming fuse.
 
  • Like
Reactions: Porto.
100A isolator or cutout doesn’t mean anything except it is rated at 100A maximum. Fuse could be 60a or 80a. If so, tails are fine.
 
  • Like
Reactions: DPG
Just checked and the main fuse is 100A...one in the middle.
 

Attachments

  • fuse.jpg
    fuse.jpg
    496.7 KB · Views: 120
The sticker indicates maximum fuse rating for the cutout. It could contain anything up to a 100A fuse.
 
  • Like
Reactions: DPG
Aaah. Ok, that makes a bit more sense thanks!
 
I’d be more worried about the fact that we have plumbers telling people they’ve been on a meter course and tamper with mains electricity
 
Hello again,
Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter, which was installed a couple of years ago (outbuildings on the second phase of a split phase supply) has been wired with 16mm tails but with a 100a isolater switch post meter. Should these have been 25mm? The installer (plumber who'd been on a meter course apparently) had no idea what i was going to install downline of this meter so shouldnt have he erred on the safe side?
Are the tails running or proposing to run through the fabric of the building ?
 
I’d be more worried about the fact that we have plumbers telling people they’ve been on a meter course and tamper with mains electricity
Apparantly it was a 'thing' with the rollout of smart meters. If you were corgi registered then the suppliers would train you up for electric meters so you could do both in one visit.
 
Are the tails running or proposing to run through the fabric of the building ?
No, just clipped to the board. I'll pull the main cutout later and see what its rating is to put this to bed.
 
Apparantly it was a 'thing' with the rollout of smart meters. If you were corgi registered then the suppliers would train you up for electric meters so you could do both in one visit.
Never heard of it

Asking plumbers to do mains electricity sounds like a recipe for disaster. Whoever thought of that idea needs to be sacked. We as electricians aren’t even allowed to touch the meter
 
Never heard of it

Asking plumbers to do mains electricity sounds like a recipe for disaster. Whoever thought of that idea needs to be sacked. We as electricians aren’t even allowed to touch the meter
This was 5 years ago so maybe things have changed since then. But whatever, nothing surprises me anymore. I lost a job once to a brazilian who'd done a 2 month 'mechatronics' course, I had 15years experience and a degree. Money talks.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Suffolk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician
Business Name
Marine electronics

Thread Information

Title
Meter Tails : Do i have a potential issue?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
clanky,
Last reply from
clanky,
Replies
11
Views
2,894

Advert