Between an OCPD tripping in the original CU as opposed to the new one.
He's got a 40amp in the LV and a proposed 63amp in the main cu.

There is partial selectivity between two MCBs up to the selectivity
limit current if the downstream MCB has a lower rated current than
the upstream MCB
 
It's a better alternative to having those tails running up the wall.

The surface installation of tails complies with the regulations but disregarding selectivity does not.

And selectivity between what ?

Between protective devices, the 63A mcb will not achieve any selectivity with the downstream MCB's.
 
He's got a 40amp in the LV and a proposed 63amp in the main cu.

There is partial selectivity between two MCBs up to the selectivity
limit current if the downstream MCB has a lower rated current than
the upstream MCB

That's not enough to give much selectivity though. Probably better in this case to split the tails as they have done in this case.
 
The surface installation of tails complies with the regulations but disregarding selectivity does not.
That's not true, there is partial selectivity if the downstream MCB has a lower rated current than the upstream MCB

There are already rcbos downstream of the 40 amp MCB, so does that mean there is no selectivity ?? Even using tails ?


Between protective devices, the 63A mcb will not achieve any selectivity with the downstream MCB's.
Not true.


Also bear in mind that these boards are next to each other.
 
Last edited:
That's not enough to give much selectivity though. Probably better in this case to split the tails as they have done in this case.
How about something like this with the outbuildings MCB omitted.

IMG_1826.jpg

73 posts on this?
FFS, if you don't like how it looks, cover it up!
Or design it properly in the beginning.
 

Reply to Do these internally exposed meter tails require mechanical protection? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

M
Hi I wonder if anyone to clear something up for me. i have a customer who wants a consumer unit located in a more convenient position for them...
Replies
18
Views
17K
522.6.101(iii) requires trunking 50x50 to BS EN 50085-2-1 . But mechanical protection (iv) : We agree that mechanical protection is "difficult to...
Replies
19
Views
11K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock