Feeding a CU from an MCB is bad practice as it gives little to no chance of selectivity.
It's a better alternative to having those tails running up the wall.

And selectivity between what ?
 
It's a better alternative to having those tails running up the wall.

And selectivity between what ?

Between an OCPD tripping in the original CU as opposed to the new one.
 
  • Like
Reactions: nicebutdim
Between an OCPD tripping in the original CU as opposed to the new one.
He's got a 40amp in the LV and a proposed 63amp in the main cu.

There is partial selectivity between two MCBs up to the selectivity
limit current if the downstream MCB has a lower rated current than
the upstream MCB
 
He's got a 40amp in the LV and a proposed 63amp in the main cu.

There is partial selectivity between two MCBs up to the selectivity
limit current if the downstream MCB has a lower rated current than
the upstream MCB

That's not enough to give much selectivity though. Probably better in this case to split the tails as they have done in this case.
 
Can't believe this is pushing 70 posts for something that essentially just looks bad.
 
The surface installation of tails complies with the regulations but disregarding selectivity does not.
That's not true, there is partial selectivity if the downstream MCB has a lower rated current than the upstream MCB

There are already rcbos downstream of the 40 amp MCB, so does that mean there is no selectivity ?? Even using tails ?


Between protective devices, the 63A mcb will not achieve any selectivity with the downstream MCB's.
Not true.


Also bear in mind that these boards are next to each other.
 
Last edited:
Next thing we'll have 50 odd posts for what drill should I use.
stick with the ones that go round and round, I have always found them ok.
 
  • Like
Reactions: timhoward
73 posts on this?
FFS, if you don't like how it looks, cover it up!
 
That's not enough to give much selectivity though. Probably better in this case to split the tails as they have done in this case.
How about something like this with the outbuildings MCB omitted.

IMG_1826.jpg

73 posts on this?
FFS, if you don't like how it looks, cover it up!
Or design it properly in the beginning.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Do these internally exposed meter tails require mechanical protection?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
75

Advert

Thread statistics

Created
drewzh,
Last reply from
mainline,
Replies
75
Views
11,230

Advert