Feeding a CU from an MCB is bad practice as it gives little to no chance of selectivity.
It's a better alternative to having those tails running up the wall.
And selectivity between what ?
Between an OCPD tripping in the original CU as opposed to the new one.
Reactions: nicebutdim
He's got a 40amp in the LV and a proposed 63amp in the main cu.
There is partial selectivity between two MCBs up to the selectivity
limit current if the downstream MCB has a lower rated current than
the upstream MCB
the upstream MCB
That's not enough to give much selectivity though. Probably better in this case to split the tails as they have done in this case.
Can't believe this is pushing 70 posts for something that essentially just looks bad.
The surface installation of tails complies with the regulations but disregarding selectivity does not.
That's not true, there is partial selectivity if the downstream MCB has a lower rated current than the upstream MCB
There are already rcbos downstream of the 40 amp MCB, so does that mean there is no selectivity ?? Even using tails ?
Between protective devices, the 63A mcb will not achieve any selectivity with the downstream MCB's.
Not true.
Also bear in mind that these boards are next to each other.
Next thing we'll have 50 odd posts for what drill should I use.
stick with the ones that go round and round, I have always found them ok.
Reactions: timhoward
73 posts on this?
FFS, if you don't like how it looks, cover it up!
How about something like this with the outbuildings MCB omitted.
73 posts on this?
Or design it properly in the beginning.
Do these internally exposed meter tails require mechanical protection?
drewzh,
mainline,