Hi all. I've done an install and carried out all tests except Ze. The site is a large electronics factory. The install is supplied from a sub board but the board supplies equipment required to be on 24/7. I've heard about contacting the DNO. Any advice would be appreciated. Thomas
 
You can contact the local DNO to your area and get the Ze by request.

And they can tell you anything they like! .8 and .35 values are little more than a target, they pretty much have carte-blanche to provide what they want as it's not actually stipulated anywhere in regulations, however the Zs values of BS7671 must be adhered to.

But if it's a private supply or a very local TX then it's going to be rock bottom - so you then have an issue of high PFC. If the place has a down-period or shift change during the day, you could always make arrangements to have a couple of minutes in which to disconnect the earth conductor in order to do the test, so long as there is no danger to users. Maybe. Needs risk assessing carefully!
 
Seems a bit over kill to try and shut down a large 24/7 electronic factory for a small install of a few circuits ( im guessing there) Take a Zdb at main board and PFC. Ask to see a recent EICR or PIR and have a look at the Ze if it was done. Just put down Zdb and move on.
 
Seems a bit over kill to try and shut down a large 24/7 electronic factory for a small install of a few circuits ( im guessing there) Take a Zdb at main board and PFC. Ask to see a recent EICR or PIR and have a look at the Ze if it was done. Just put down Zdb and move on.

Just re-read the OP, and yes, as it's a sub then Zdb and go home!
 
What! you mean the DNO dont have a room filled with dusty filling cabinets covered in cob webs, with a draw in each, all neatly compartmentalised, in alphabetical order for every installation within the whole of Great Britain. No, they cant be as disorganised as me, can they?
 
What! you mean the DNO dont have a room filled with dusty filling cabinets covered in cob webs, with a draw in each, all neatly compartmentalised, in alphabetical order for every installation within the whole of Great Britain. No, they cant be as disorganised as me, can they?

I know its impracticable and near enough impossible. But when you think about it, and what the DNO actually represent...they bloody well should have a database that size lol.

I love ringing the DNO. Not.
 
DNOs are hopeless....mine decided to wait until the supply gave up before coming out to do a repair....despite the property lights in question flickering like some insane disco, motor speeds hitting the deck etc.
Got a right raving at down the phone, particularly as the resident is disabled....that got their attention....and a quick 180 in attitude...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Unable to measure Ze
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
thomas-1981,
Last reply from
thomas-1981,
Replies
15
Views
3,115

Advert

Back
Top