Hi all

Just got a metrel mi3000. Was using it today to test a new cu job. But I'm confused...when I do continuity tests on a ring I can do tests on the crossed line and neutral using the plug adaptor but I can't use the plug adapter to do test on crossed earth and line!?
This means I have to open up the socket and use the probes.
Am I missing something. Is there a way of changing the setting so that it tests between line and earth?
Any thoughts? Cheers.
 
What do you mean?

to quote you:

"Just got a metrel mi3000. Was using it today to test a new cu job. But I'm confused...when I do continuity tests on a ring I can do tests on the crossed line and neutral using the plug adaptor but I can't use the plug adapter to do test on crossed earth and line!?"

So you've changed a CU and you aren't sure how the tester works. Please tell me this is your own home.
 
Hi all

Just got a metrel mi3000. Was using it today to test a new cu job. But I'm confused...when I do continuity tests on a ring I can do tests on the crossed line and neutral using the plug adaptor but I can't use the plug adapter to do test on crossed earth and line!?
This means I have to open up the socket and use the probes.
Am I missing something. Is there a way of changing the setting so that it tests between line and earth?
Any thoughts? Cheers.

Ben,

If it is anyhing like their MI3002 then the only way to do what you want to do is to get hold of a KEWTECH kewcheck R2 plug or similar. Then plug the line and neutral leads from the METREL into the L(R1) and E(R2) sockets on the back of the 3-pin plug allowing your to do R1 + R2 measurements. I emailed METREL to suggest that it is misleading to do what purports to be an R1 + R2 ie Line and Circuit Protective Conductor test using line and neutral probes.

Yours Aye

GB
 
I know how it works. But with say a kewtech tester you could swap out the leads connected to the plug adapter to perform the test whereas with the metrel it is all fixed so you can't specify which points of the socket you want to test. I don't mind using the probes but it just takes longer. Do you have a mi3000?
 
Thanks for that gb.kayak. Apparently I'm not as mad as I'm being made out to be. I'll look into the kewtech plug.
Cheers.
 
I emailed METREL to suggest that it is misleading to do what purports to be an R1 + R2 ie Line and Circuit Protective Conductor test using line and neutral probes.
What on earth (no pun intended) do you mean by that mate? It's a bog standard 3 lead tester carrying out a bog standard continuity test. There's no difference in carrying out an R1+R2 test than any other 2 lead continuity test.
 
To the OP, if you're getting an answer on one part of a continuity test but not on another what does that tell you?
 
Osg says on a ring you are supposed to test l to l, n to n, cpc to cpc and then cross l to n and l to cpc. With the metrel you can't test at the plug end for l to cpc. That is the point I am making.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
using metrel mi3000 to do ring continuity test
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
55

Advert

Thread statistics

Created
ben.l,
Last reply from
DPG,
Replies
55
Views
19,352

Advert

Back
Top