amckay

My neighbour asked me to put some fancy switch plates up after he decorated. So I'm screwing the plate into the back box and Bang! I mustn't of tightened a connection properly (prob should have turned circuit off too lol) :-( so I make everything ok and re energise circuit but lights for that switch won't illuminate. Change of bulbs reveals its still not working. I've used a non contact voltage detector to check there is power to the lamps and have checked continuity using a fluke t90 and some old offcut to make up the distance and continuity is fine on both L+N. I can't do IR as my tester has been sent away for calibration with screwfix.
I've never come across this before and so far I'm stumped. Any ideas where the fault lies?
 
First of all you need proper test leads , then get an Electrician to use them ,,
If your using a volt stick , this would light up anyway as the neutral is still connected through other lamps ,
Other point is You should not have been messing with this live ,
 
First of all you need proper test leads , then get an Electrician to use them ,,
If your using a volt stick , this would light up anyway as the neutral is still connected through other lamps ,
Other point is You should not have been messing with this live ,

I have proper test leads that are attached to my meter which is in a calibration workshop somewhere in north Manchester. I am an electrician. Voltstick = fair point. I had it live as I did I functional test, just didn't bother screwing it back while circuit was dead.
 
My neighbour asked me to put some fancy switch plates up after he decorated. So I'm screwing the plate into the back box and Bang! I mustn't of tightened a connection properly (prob should have turned circuit off too lol) :-( so I make everything ok and re energise circuit but lights for that switch won't illuminate. Change of bulbs reveals its still not working. I've used a non contact voltage detector to check there is power to the lamps and have checked continuity using a fluke t90 and some old offcut to make up the distance and continuity is fine on both L+N. I can't do IR as my tester has been sent away for calibration with screwfix.
I've never come across this before and so far I'm stumped. Any ideas where the fault lies?

Do you have a proper GS38 voltage indicator?
 
My neighbour asked me to put some fancy switch plates up after he decorated. So I'm screwing the plate into the back box and Bang! I mustn't of tightened a connection properly (prob should have turned circuit off too lol) :-( so I make everything ok and re energise circuit but lights for that switch won't illuminate. Change of bulbs reveals its still not working. I've used a non contact voltage detector to check there is power to the lamps and have checked continuity using a fluke t90 and some old offcut to make up the distance and continuity is fine on both L+N. I can't do IR as my tester has been sent away for calibration with screwfix.
I've never come across this before and so far I'm stumped. Any ideas where the fault lies?

Do you have a proper GS38 voltage indicator?

Yes. Fluke T90 as mentioned in OP.
 
Yes. Fluke T90 as mentioned in OP.

Fair enough, didn't recognise it, thought it might be a mutleymeter. I would safe isolate then short the live feed and switched lives at the switch, in junction block or the same terminal on the switch, then deisolate. If the lights don't then come on, I would be carefully checking with the Fluke whether there was 230V between the junction I just made and earth. Then the same between switched live and earth up at the light fitting. You said you checked live and neutral continuity with the Fluke but bear in mind it only draws what, 3mA? Maybe what with your shorting out calamity you have some medium-impedance continuity there, bad contact or something, that looks OK on the Fluke or with the non contact tester with no current draw, but is too much to get current for the lights through. Maybe you have 230V live to neutral up at the lights with no bulbs in but when you load it with a bulb it's collapsing.
 
Last edited by a moderator:
Thanks nickD
Personally I'd like to throw a new cable in but its just been redecorated IMHO the GAF needs a rewire, like my house next door did.
When I moved in the 7kw shower was on 2.5mm cable. Should have seen the blackened cable behind the DP isolater pull cord.... Rough stuff
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
wall light fault
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
99
Unsolved
--

Advert

Thread statistics

Created
amckay,
Last reply from
GLENNSPARK,
Replies
99
Views
10,003

Advert

Back
Top