metal capping not needed according to 17th

Discuss metal capping not needed according to 17th in the Electricians' Talk area at ElectriciansForums.net

Reaction score
0
Is metal capping required on a new installation in a house to protect the cables if a rcd is used ? According to two lads who i work with have done there 17th ed last week it is not needed so is it only for protexting cables while been plastered ?
 
It is not required. Favoured,specified,preferred,but not required. Careful plasterers negate its use...:icon12:
 
Is metal capping required on a new installation in a house to protect the cables if a rcd is used ? According to two lads who i work with have done there 17th ed last week it is not needed so is it only for protexting cables while been plastered ?

As already said, never required but often used.
It cannot be used as mechanical protection for the cables if not RCD protected and buried less than 50mm
 
if someone was to bang a nail the capping wont help. but it will make extracting the cable for repair much harder.
i`m filling my chases with some bonding coat, no cables on show when plasterer comes do his job, no problems later.
 
capping is pointless really, but is something most electricians like myself like to do.
i thought there was once a reg, for reasonable protection from the plasterers trowel.
 
I always thought it was a rule of thumb or best practice, If the width of the chase is greater than 3/4 of the width of the plasters trowel capping is needed???
 
It would be wise to use plastic capping on bare inners leafs that are going to be floated. It keeps the cables tidy and together (if there is more than one) and gives enough protection against a trowel, its common sense really.
 
Well I have heard it all now, I think the trainee section should snap this fella up sharpish not!!
 
whats wrong with putting a bit of conduit in so you can actually get the wires pulled in/out without bashing the house into submission?
just a thought.
 
We always install capping when we wire in singles however.

Omg fellas. Really? Sometimes it is too easy on here.

Bad move. Two options here, either you are making a genuine statement and are clueless about installation techniques or you're making false statements which means you're trolling. Either way you're on thin ice so don't do it again.

Please be warned!!

Threads and posts get indexed by search engines and misleading statements like this end up carrying weight in Google search results because they supposedly come from professional electricians. If you want to start some banter keep it in the Chit Chat forum where it belongs not in the Electrical forums. Also if there's threads closed and posts deleted and your trolling is the cause of it then you'll be shown the door.
 
whats wrong with putting a bit of conduit in so you can actually get the wires pulled in/out without bashing the house into submission?
just a thought.
And how exactly do you propose to hide a bloody great lump of metal conduit?
Obviously plastic oval conduit is a different thing entirely but you're still cutting a chase.
 
whats wrong with putting a bit of conduit in so you can actually get the wires pulled in/out without bashing the house into submission?
just a thought.

Well thats the beauty of the oval tube.
i find capping easier to fix however, and keeps cables neat and tidy and secure.
 
Bad move. Two options here, either you are making a genuine statement and are clueless about installation techniques or you're making false statements which means you're trolling. Either way you're on thin ice so don't do it again.

Please be warned!!

Threads and posts get indexed by search engines and misleading statements like this end up carrying weight in Google search results because they supposedly come from professional electricians. If you want to start some banter keep it in the Chit Chat forum where it belongs not in the Electrical forums. Also if there's threads closed and posts deleted and your trolling is the cause of it then you'll be shown the door.

Please accept my apology. I did not think of it that way. TBH I really thought it was an obvious joke and thought it would be taken as such.

I have edited my post and made it clear why.

let me be clear. This is absolutely not acceptable practice and should never be followed.
 

Reply to metal capping not needed according to 17th in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock