Currently reading:
Bonding Gas Supply in an Outbuilding
Discuss Bonding Gas Supply in an Outbuilding in the UK Electrical Forum area at ElectriciansForums.net
P
Piratepete
Hi Guys
Doing an EICR of a property.
The client has an outbuilding with gas and water supplies. It has it's own CU fed from the main CU in the house.
The water is bonded but the gas is not.
The water supply is underground from the house in plastic and then changes to copper which is bonded.
The gas supply comes from the house in an underground copper pipe linked to the gas pipes in the house. So, electrically, it would be subject to the bonding in the house.
But does this negate the need to bond it in the outbuilding?
Looking forward to wise words!
Cheers
Pete:confused:
Why are you asking where equivalent conductance is mentioned when you go on to mention equivalent conductance yourself in you second paragraph.
I have no issue with their being other interpretations or however you wish to describe it. If you can provide links to the published documents/guidance which could be referenced if I did not follow the IETs guidance notes and I did have to defend my installation in court then I will consider using that guidance in my work.
Dave the first paragragh asks for the CSA to be half that of the Earthing conductor, so lets say the Earthing conductor need to be 20mm, would a 10mm steel Main protective bonding conductor be okay?
Cheers
Cheers
If the required earthing conductor is 20mm steel and PME conditions do not apply then yes a 10mm steel main bond would be okay according to 544.1.1
But it would not comply if it is a seperate conductor (543.2.4)
And yes a main bond is included in the definition of a protective conductor (see definitions page.33)
Well no it wouldnt, a protective conductor 10mm or less needs to be copper 543.2.4.
Cheers
Dave could you explain this bit?
Cheers
A seperate conductor would be a conductor which does not form part of a cable or multicore cable and is not trunking, ducting, conduit. It's pretty clear if you read that regulation properly. It states that it only applies to the specified types of conductor referenced in parts of an above regulation.
Okay, so 543.2.4 takes us to 543.2.1 (i) to (v) agreed?
So how do you interpret 543.2.1, " A protective conductor may consist of one or more of the following"?
Cheers
Calculating the steel CSA required for a main bond is not the same as calculating the steel CSA required for a CPC. The requirement is that the steel CSA must give the same conductance as the required copper main bond. The calculation for working this out is given in guidance note 8 page 55, but it is basically the steel CSA must be greater than the product of the required copper CSA and the ratio of the resistivities of copper and steel.
The ratio of the resisitivities of copper and steel is given as 8.5, so the required minimum CSA of steel to be equivalent to a 10mm copper main bond is 8.5x10=85mm
That 6mm 4 core isn't looking so good really is it!
I was responding to the post that suggested using both the 6mm core and the SWA armour, which would mean the SWA would only require an equivilent conductance of 4mm copper.
I use the ratio of 1:9 when calculating.
Reference to copper equivalence is made in BS7671 when determining the CSA of bonding conductors where PME conditions apply.
Cheers
I interpret that as meaning a protective conductor could be made up of one or more of the listed items. So for example it could be that the sheath of an MI cable forms the protective conductor up to the point where the gland connects it to galv trunking which then also forms part of that protective conductor.
I think you are steering this in the direction of the earlier question as to whether it is acceptable to use 2 conductors of different materials and CSAs in parallel as a bonding conductor. And I concede that you could interpret this regulation as allowing it, but I whether or not that is the 'intent of the regulation' I don't know.
Hi Guys
It's the OP here! Fascinating and thought provoking discussion, not entirely clear.
FYI
1. The installation is PME
2. The SWA cable is XLPE 3 core, not 4.
3. I used a C3 with NICEIC Technical Support's blessing
4. My table gives the equivalent Cu size of the armour as 7.39 sqmm. Is that correct?
5. Under PME rules, I understand that the CPC should be 10mm. Is that correct?
6. As neither the core nor the wire armour are individually 10mm, is it your conclusion that they may be combined? If so, how do you calculate their combined Cu value?
Cheers
Pete
Hi Guys
FYI
Cheers
Pete
This is the argument that is raging lol, the regs say we cannot combine them, different materials ;), GN8 says not, they each have to comply in their own right, ie. 10mm ,or equivalent for the armourings.
This was partly my fault because I originally looked at a dodgy table which was over optimistic on the copper equivalent of the armourings. ;)
Geoff seems to think you can, lol
You can C3 anyway if the conductors are not showing any distress, degradation, thermal or otherwise and not less than 6mm.
Hi Guys
FYI
Cheers
Pete
1, Okay
2, Okay
3, Okay
4 That depends upon what k factors you have used, as a general rule you take the aromuring to be at 10 C less than the Line, so 60C.
4,The CPC? Do you mean Earthing conductor or Main protectine Bonding?
5, If PME, there is a risk of divereted neutral current circulating in the armour, this creates a heating effect I2R and can effect the Temp of other conductors contained within the cable. Can you use seperate the armour and a core to meet the requirements, the regs allow this!
6, You may struggle to convince your inspector to accept anthing different than equivalent conductance, so use a ratio of 8-1.
Spark68, do you have a regulation number which states
Cheers
Cheers
Oh! god not again, you cannot split the functional requirements of a single protective conductor across different materials.
In this case
Armour complies to equivalent 10mm copper = fine
core complies to 10mm = fine
Neither complies not fine
the other parts of that section
Armour complies as CPC and core complies with bonding conductor = fine
core complies as CPC and armour complies with bonding (if not causing heating) = fine
Neither comply on their own = not fine ie. cannot be combined to make up csa, they do not conduct nor current share equally.
I believe there was an article in wiring matters about this a while back, read the regs table 54.8 for PME, don't just pick one reg in isolation, you have to take that section together, failing that look at GN8
The ratio given for copper:steel is 1:8.5 in GN8, it also gives the ratio for aluminium but I don't know it off the top of my head
Some even quote 9, It can vary quite considerably, copper wire isnt that pure and becomes less conductive and when you realise what it is you are trying to acheive it becomes a little arbitrary.
Cheers
In this case
So how is it you can use an individual core of the swa(copper) and the armour(steel) together as a cpc?
Cheers
Cheers
Arghh! we don't, either the core complies, OR the armourings comply for a "straight" CPC, that is what we have been saying, the armourings are earthed for protective reasons where a core is used as the CPC, NOT to make up the csa.
Sometimes we use a core for a bonding conductor, and the armourings as the CPC, so long as both comply csa wise for their respective functions, ie. as two separate protective conductors, both (in their own right) fulfilling two different roles.
Wtf? How do you prevent them both fulfilling both functions? They'll be connected together at both ends.
They may well be physically connected, but need to be assessed for compliance individually, as in the OPs case in this long thread, the armourings may well comply as a CPC, but not as a MPB, so ideally he would need a 10mm core to fulfil the MPB part, this is what you yourself were putting forward when I looked up that iffy table.
That is not what I was putting forward earlier, what was saying earlier was that the main bond should not be made up of multiple conductors added together.
The 10mm core would become the cpc and the main bond by default, the armour would only need bonding at one end, but could be connected at both to improve the cpc.
Reply to Bonding Gas Supply in an Outbuilding in the UK Electrical Forum area at ElectriciansForums.net