Reg 542.1.3.3

Where a number of installations have separate earthing arrangements, any protective conductors common to any of these installations shall either be capable of carrying the maximum fault current likely to flow through them or be earthed within one installation only and insulated from the earthing arrangements of any other installation. In the latter circumstances, if the protective conductor forms part of the cable, the protective conductor shall be earthed only in the installation containing the associated protective device.
 
To be honest this type of situation is one of the few times TT ing the far end is worth considering on economic grounds due to the cable sizes involved, probably not in domestic where the distances are fairly short, but certainly in cases where you may only want say a lamp in an outbuilding containing plant that may be some considerable distance from the main building.
 
Then why the blanket statement ?

543.2.5 The metal covering including the sheath (bare or insulated) of a cable, in particular the sheath of a mineral insulated cable, trunking and ducting for electrical purposes and metal conduit, may be used as a protective conductor for the associated circuit, if it satisfies both requirements of items (i) and (ii) of reg 543.2.2

543.2.2 this reg is actually more about switchgear and bus bar trunking etc. but the salient points here are (i) and (ii)

(i) Its electrical continuity shall be assured, by construction or by suitable connection, in such a way as to be protected against mechanical, chemical or electrochemical deterioration.

(ii) Its cross sectional area shall be at least equal to that resulting from 543.1, or verified by test in accordance with the appropriate part of BSEN 61439 series.


What this is basically saying is that if the armouring is of insufficient csa to satisfy its use as a protective conductor, you cannot make up the difference with another undersized protective conductor, either the armouring has to comply on its own for its intended purpose, or the other protective conductor has to comply the same way. as an example of what would not be allowed, consider you need a CPC of say 10mm, and you calculate your armouring works out as a copper equivalent of 6mm, you cannot just add another CPC or core of 4mm to make up the difference, you would need the additional CPC or core to be 10mm on its own.

You can use both where for instance the armouring would comply as a CPC and a core for the MPB purposes, or vice versa.
This is one reason why you sometimes see a 10mm G/Y cable running along side an armoured cable.

Of course you can, you just need to calculate the current sharing between the two cpc.

Cheers
 
Well, if you use a 6mm 3 core SWA cable, the minimum armour CSA would have to be 36mm.
That's the CSA of the armour on a 6mm 4 core.
Might just as well use two of the 6mm cores instead.
 
Well, if you use a 6mm 3 core SWA cable, the minimum armour CSA would have to be 36mm.
That's the CSA of the armour on a 6mm 4 core.
Might just as well use two of the 6mm cores instead.

Calculating the steel CSA required for a main bond is not the same as calculating the steel CSA required for a CPC. The requirement is that the steel CSA must give the same conductance as the required copper main bond. The calculation for working this out is given in guidance note 8 page 55, but it is basically the steel CSA must be greater than the product of the required copper CSA and the ratio of the resistivities of copper and steel.

The ratio of the resisitivities of copper and steel is given as 8.5, so the required minimum CSA of steel to be equivalent to a 10mm copper main bond is 8.5x10=85mm

That 6mm 4 core isn't looking so good really is it!
 
There is no way you can use/combine two different metals types to make up any shortfall in required minimum CSA/mm. I can't believe that someone is actually talking about calculating the fault current share between between copper and steel CPC's.


If neither the copper conductor or the Steel conductor has sufficient CSA (eg A SWA cable using a 3rd core as the CPC etc) singly/in it's own right to fulfill the requirements of it's CPC or CPC/Main Bonding Conductor. Then you CANNOT combine the two CSA's of the copper conductor and the steel armouring!! I'm quite amazed really, that any experienced electrician would even think that this was an acceptable solution!!
 
There is no way you can use/combine two different metals types to make up any shortfall in required minimum CSA/mm. I can't believe that someone is actually talking about calculating the fault current share between between copper and steel CPC's.


If neither the copper conductor or the Steel conductor has sufficient CSA (eg A SWA cable using a 3rd core as the CPC etc) singly/in it's own right to fulfill the requirements of it's CPC or CPC/Main Bonding Conductor. Then you CANNOT combine the two CSA's of the copper conductor and the steel armouring!! I'm quite amazed really, that any experienced electrician would even think that this was an acceptable solution!!

It may smack of bad design, but there are no technical reasons not to do so, nor do the regs prevent it.

Calculating current sharing is well documented, and there is a specific guidance for SWA and a parallel Protective conductors.


Maybe you could give a technical reason for your opinion?

Cheers
 
Calculating the steel CSA required for a main bond is not the same as calculating the steel CSA required for a CPC. The requirement is that the steel CSA must give the same conductance as the required copper main bond. The calculation for working this out is given in guidance note 8 page 55, but it is basically the steel CSA must be greater than the product of the required copper CSA and the ratio of the resistivities of copper and steel.

The ratio of the resisitivities of copper and steel is given as 8.5, so the required minimum CSA of steel to be equivalent to a 10mm copper main bond is 8.5x10=85mm

That 6mm 4 core isn't looking so good really is it!

Dave, thats one interpretation, not hte only one though! Read the first paragraph and note the full stop. So excluding PME, the csa need to be half that of the earthing conductor. Where does it state equivalent conductance to that of copper, what about steel, aluminium etc?

Then you have the second paragraph which states you need not exceed 25mm if Cu or a csa in another metal offereing equivalent conductance.


Cheers
 
Last edited by a moderator:
It may smack of bad design, but there are no technical reasons not to do so, nor do the regs prevent it.

Calculating current sharing is well documented, and there is a specific guidance for SWA and a parallel Protective conductors.


Maybe you could give a technical reason for your opinion?

Cheers

Maybe, if both parallel conductors are of the SAME size and Same metal, but current sharing across two different sized conductors is a no, no!! ...And if then, they are made up of two different metals, Nah, bloody ridiculous!!


Perhaps you can post this specific guidance for SWA and parallel protective conductors... Because something is very wrong somewhere if it's supporting your criteria of a mix and match set up....

This is not MY opinion, just think about it for a nano second, what path is a fault current liable to take, given the choice of a copper or galv steel conductor?? Do you actually believe, the current will divide itself in accordance with any calculations?? lol!!
 
Dave, thats one interpretation, not hte only one though! Read the first paragraph and note the full stop. So excluding PME, the csa need to be half that of the earthing conductor. Where does it state equivalent conductance to that of copper, what about steel, aluminium etc?

Then you have the second paragraph which states you need not exceed 25mm if Cu or a csa in another metal offereing equivalent conductance.


Cheers

Hell's Bell's!!

It's an interpretation that just happens to be correct, not that, that should make any difference to you....
 
Hell's Bell's!!

It's an interpretation that just happens to be correct, not that, that should make any difference to you....

Well, why dont we need to check the thermal constraints of a bonding conductor? Well it because the assumption is there will be little current flow, we just need to transfer potential, so if the assumption is little current flow, why do we need to consider conductance or inversely the resistance?

Now the GN Author, goes along with Daves interpretation, but many Engineers incuding some at the IET interpret this a little differently.

So, as i said if you could offer a technical response, that would be much appreciated.

Ive also PM you the report on SWA and parallel protevtive conductors, enjoy your read!

Cheers
 
Now the GN Author, goes along with Daves interpretation, but many Engineers incuding some at the IET interpret this a little differently.

Ive also PM you the report
on SWA and parallel protevtive conductors, enjoy your read!

Cheers

Any of these many Engineers published anything on this other interpretation??

Already sent my reply on this report, which has been discussed here before...
 
Any of these many Engineers published anything on this other interpretation??

Already sent my reply on this report, which has been discussed here before...

Not that im aware of, ill have a peruse.

With regard to the report, ERA are responsible for the current ratings in appendix 4 of BS7671, and as i said cable manufacturers also support the reports.

But you have yet to offer any technical supports for your stance.

Cheers
 
Not that im aware of, ill have a peruse.

With regard to the report, ERA are responsible for the current ratings in appendix 4 of BS7671, and as i said cable manufacturers also support the reports.

But you have yet to offer any technical supports for your stance.

Cheers

Strange then that manufacturers Current ratings are generally found to be different (generally higher) than those listed/tabulated in BS7671. In fact i've rarely used BS7671 current ratings for several years now, preferring to use for obvious reasons manufacturer's published ratings....

No real need for Tech support is there, surely common sense should be smacking you round the head, around about now??
 
Strange then that manufacturers Current ratings are generally found to be different (generally higher) than those listed/tabulated in BS7671. In fact i've rarely used BS7671 current ratings for several years now, preferring to use for obvious reasons manufacturer's published ratings....

No real need for Tech support is there, surely common sense should be smacking you round the head, around about now??


Correct, manufactures use the ERA ratings, which have factors applied to them, if you apply the same conditions that the ERA set out to the BS7671 ratings you will get the same ratings.

They are responsible for most of appendix 4, grouping factors etc. No common senese required just good engineering.

Teh cable manufacturers, the IET support many of the ERA work, thats god enough for me.

As isaid if you can provide technical support for you stance tehn we can continue the debate, otherwise we will have to agree to disagree.

Cheers
 
Correct, manufactures use the ERA ratings, which have factors applied to them, if you apply the same conditions that the ERA set out to the BS7671 ratings you will get the same ratings.

They are responsible for most of appendix 4, grouping factors etc. No common senese required just good engineering.

Teh cable manufacturers, the IET support many of the ERA work, thats god enough for me.

As isaid if you can provide technical support for you stance tehn we can continue the debate, otherwise we will have to agree to disagree.

Cheers

Hey, if you wish to believe anything and everything that has been put in print, who am i to tell you that would be foolish!!

Manufactures use their own specifications and data, that includes current carrying ratings!! Do you think that the cable manufactures only supply the UK, or that their current ratings for a given cable type/size are based solely on or around ERA/British Standards?? Now that is being naive!!
 
Dave, thats one interpretation, not hte only one though! Read the first paragraph and note the full stop. So excluding PME, the csa need to be half that of the earthing conductor. Where does it state equivalent conductance to that of copper, what about steel, aluminium etc?

Then you have the second paragraph which states you need not exceed 25mm if Cu or a csa in another metal offereing equivalent conductance.


Cheers

Why are you asking where equivalent conductance is mentioned when you go on to mention equivalent conductance yourself in you second paragraph.

I have no issue with their being other interpretations or however you wish to describe it. If you can provide links to the published documents/guidance which could be referenced if I did not follow the IETs guidance notes and I did have to defend my installation in court then I will consider using that guidance in my work.
 
Why are you asking where equivalent conductance is mentioned when you go on to mention equivalent conductance yourself in you second paragraph.

I have no issue with their being other interpretations or however you wish to describe it. If you can provide links to the published documents/guidance which could be referenced if I did not follow the IETs guidance notes and I did have to defend my installation in court then I will consider using that guidance in my work.

Dave the first paragragh asks for the CSA to be half that of the Earthing conductor, so lets say the Earthing conductor need to be 20mm, would a 10mm steel Main protective bonding conductor be okay?

Cheers
 
Dave the first paragragh asks for the CSA to be half that of the Earthing conductor, so lets say the Earthing conductor need to be 20mm, would a 10mm steel Main protective bonding conductor be okay?

Cheers

If the required earthing conductor is 20mm steel and PME conditions do not apply then yes a 10mm steel main bond would be okay according to 544.1.1

But it would not comply if it is a seperate conductor (543.2.4)

And yes a main bond is included in the definition of a protective conductor (see definitions page.33)
 
If the required earthing conductor is 20mm steel and PME conditions do not apply then yes a 10mm steel main bond would be okay according to 544.1.1

But it would not comply if it is a seperate conductor (543.2.4)

And yes a main bond is included in the definition of a protective conductor (see definitions page.33)


Well no it wouldnt, a protective conductor 10mm or less needs to be copper 543.2.4.

Cheers
 
Dave could you explain this bit?

But it would not comply if it is a seperate conductor (543.2.4)

Cheers

A seperate conductor would be a conductor which does not form part of a cable or multicore cable and is not trunking, ducting, conduit. It's pretty clear if you read that regulation properly. It states that it only applies to the specified types of conductor referenced in parts of an above regulation.
 
A seperate conductor would be a conductor which does not form part of a cable or multicore cable and is not trunking, ducting, conduit. It's pretty clear if you read that regulation properly. It states that it only applies to the specified types of conductor referenced in parts of an above regulation.

Okay, so 543.2.4 takes us to 543.2.1 (i) to (v) agreed?

So how do you interpret 543.2.1, " A protective conductor may consist of one or more of the following"?

Cheers
 
Calculating the steel CSA required for a main bond is not the same as calculating the steel CSA required for a CPC. The requirement is that the steel CSA must give the same conductance as the required copper main bond. The calculation for working this out is given in guidance note 8 page 55, but it is basically the steel CSA must be greater than the product of the required copper CSA and the ratio of the resistivities of copper and steel.

The ratio of the resisitivities of copper and steel is given as 8.5, so the required minimum CSA of steel to be equivalent to a 10mm copper main bond is 8.5x10=85mm

That 6mm 4 core isn't looking so good really is it!
I was responding to the post that suggested using both the 6mm core and the SWA armour, which would mean the SWA would only require an equivilent conductance of 4mm copper.
I use the ratio of 1:9 when calculating.

Reference to copper equivalence is made in BS7671 when determining the CSA of bonding conductors where PME conditions apply.
 
Last edited by a moderator:
You didn't specify whether it was a seperate conductor or the armour of a cable/conduit/trunking. Which is why I said it may not comply according to 543.2.4

Dave he's just baiting people, no matter what you say it'll be twisted in way or the other. leave to his own devises...
 
Dave he's just baiting people, no matter what you say it'll be twisted in way or the other. leave to his own devises...


Twisting,baiting, i dont thinks so! I try to give facts and back them up, not self opinionated views with no technical foundation! And im sure dave can answer for himself!
 
Okay, so 543.2.4 takes us to 543.2.1 (i) to (v) agreed?

So how do you interpret 543.2.1, " A protective conductor may consist of one or more of the following"?

Cheers

I interpret that as meaning a protective conductor could be made up of one or more of the listed items. So for example it could be that the sheath of an MI cable forms the protective conductor up to the point where the gland connects it to galv trunking which then also forms part of that protective conductor.

I think you are steering this in the direction of the earlier question as to whether it is acceptable to use 2 conductors of different materials and CSAs in parallel as a bonding conductor. And I concede that you could interpret this regulation as allowing it, but I whether or not that is the 'intent of the regulation' I don't know.
 
Hi Guys
It's the OP here! Fascinating and thought provoking discussion, not entirely clear.
FYI
1. The installation is PME
2. The SWA cable is XLPE 3 core, not 4.
3. I used a C3 with NICEIC Technical Support's blessing
4. My table gives the equivalent Cu size of the armour as 7.39 sqmm. Is that correct?
5. Under PME rules, I understand that the CPC should be 10mm. Is that correct?
6. As neither the core nor the wire armour are individually 10mm, is it your conclusion that they may be combined? If so, how do you calculate their combined Cu value?

Cheers
Pete
 
Hi Guys
It's the OP here! Fascinating and thought provoking discussion, not entirely clear.
FYI
1. The installation is PME
2. The SWA cable is XLPE 3 core, not 4.
3. I used a C3 with NICEIC Technical Support's blessing
4. My table gives the equivalent Cu size of the armour as 7.39 sqmm. Is that correct?
5. Under PME rules, I understand that the CPC should be 10mm. Is that correct?
6. As neither the core nor the wire armour are individually 10mm, is it your conclusion that they may be combined? If so, how do you calculate their combined Cu value?

Cheers
Pete

This is the argument that is raging lol, the regs say we cannot combine them, different materials ;), GN8 says not, they each have to comply in their own right, ie. 10mm ,or equivalent for the armourings.

This was partly my fault because I originally looked at a dodgy table which was over optimistic on the copper equivalent of the armourings. ;)

Geoff seems to think you can, lol

You can C3 anyway if the conductors are not showing any distress, degradation, thermal or otherwise and not less than 6mm.
 
Hi Guys
It's the OP here! Fascinating and thought provoking discussion, not entirely clear.
FYI
1. The installation is PME
2. The SWA cable is XLPE 3 core, not 4.
3. I used a C3 with NICEIC Technical Support's blessing
4. My table gives the equivalent Cu size of the armour as 7.39 sqmm. Is that correct?
5. Under PME rules, I understand that the CPC should be 10mm. Is that correct?
6. As neither the core nor the wire armour are individually 10mm, is it your conclusion that they may be combined? If so, how do you calculate their combined Cu value?

Cheers
Pete

1, Okay
2, Okay
3, Okay
4 That depends upon what k factors you have used, as a general rule you take the aromuring to be at 10 C less than the Line, so 60C.
4,The CPC? Do you mean Earthing conductor or Main protectine Bonding?
5, If PME, there is a risk of divereted neutral current circulating in the armour, this creates a heating effect I2R and can effect the Temp of other conductors contained within the cable. Can you use seperate the armour and a core to meet the requirements, the regs allow this!
6, You may struggle to convince your inspector to accept anthing different than equivalent conductance, so use a ratio of 8-1.


Spark68, do you have a regulation number which states
the regs say we cannot combine them, different materials

Cheers
 
If I drive round there and bond it myself for free can we end this post lol
Yeah. Ok. I'll shut up now. At some time I'll have to go round and install a 10 mm bonding wire between the outbuilding and the house. I'm thinking that an overhead one would be easiest. Any rules against that?:biggrin:
Cheers
Pete
 
Spark68, do you have a regulation number which states

Cheers

Oh! god not again, you cannot split the functional requirements of a single protective conductor across different materials.

In this case
Armour complies to equivalent 10mm copper = fine
core complies to 10mm = fine

Neither complies not fine

the other parts of that section

Armour complies as CPC and core complies with bonding conductor = fine
core complies as CPC and armour complies with bonding (if not causing heating) = fine

Neither comply on their own = not fine ie. cannot be combined to make up csa, they do not conduct nor current share equally.

I believe there was an article in wiring matters about this a while back, read the regs table 54.8 for PME, don't just pick one reg in isolation, you have to take that section together, failing that look at GN8
 
The ratio given for copper:steel is 1:8.5 in GN8, it also gives the ratio for aluminium but I don't know it off the top of my head

Some even quote 9, It can vary quite considerably, copper wire isnt that pure and becomes less conductive and when you realise what it is you are trying to acheive it becomes a little arbitrary.

Cheers
 
Oh! god not again, you cannot split the functional requirements of a single protective conductor across different materials.

In this case
Armour complies to equivalent 10mm copper = fine
core complies to 10mm = fine

Neither complies not fine

the other parts of that section

Armour complies as CPC and core complies with bonding conductor = fine
core complies as CPC and armour complies with bonding (if not causing heating) = fine

Neither comply on their own = not fine ie. cannot be combined to make up csa, they do not conduct nor current share equally.

I believe there was an article in wiring matters about this a while back, read the regs table 54.8 for PME, don't just pick one reg in isolation, you have to take that section together, failing that look at GN8

So how is it you can use an individual core of the swa(copper) and the armour(steel) together as a cpc?


Cheers
 
So how is it you can use an individual core of the swa(copper) and the armour(steel) together as a cpc?


Cheers

Arghh! we don't, either the core complies, OR the armourings comply for a "straight" CPC, that is what we have been saying, the armourings are earthed for protective reasons where a core is used as the CPC, NOT to make up the csa.

Sometimes we use a core for a bonding conductor, and the armourings as the CPC, so long as both comply csa wise for their respective functions, ie. as two separate protective conductors, both (in their own right) fulfilling two different roles.
 
Sometimes we use a core for a bonding conductor, and the armourings as the CPC, so long as both comply csa wise for their respective functions, ie. as two separate protective conductors, both (in their own right) fulfilling two different roles.

Wtf? How do you prevent them both fulfilling both functions? They'll be connected together at both ends.
 
Wtf? How do you prevent them both fulfilling both functions? They'll be connected together at both ends.

They may well be physically connected, but need to be assessed for compliance individually, as in the OPs case in this long thread, the armourings may well comply as a CPC, but not as a MPB, so ideally he would need a 10mm core to fulfil the MPB part, this is what you yourself were putting forward when I looked up that iffy table.
 
Going back some now but im pretty sure mines and quarys required more stringent impedances to keep touch voltages down, some of the strands in the amouring were copper?

Or am i getting confused.

Cheers
 
They may well be physically connected, but need to be assessed for compliance individually, as in the OPs case in this long thread, the armourings may well comply as a CPC, but not as a MPB, so ideally he would need a 10mm core to fulfil the MPB part, this is what you yourself were putting forward when I looked up that iffy table.

That is not what I was putting forward earlier, what was saying earlier was that the main bond should not be made up of multiple conductors added together.

The 10mm core would become the cpc and the main bond by default, the armour would only need bonding at one end, but could be connected at both to improve the cpc.
 

Reply to Bonding Gas Supply in an Outbuilding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
925
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock