Have you designed this to stay off until it is reset by a deliberate action, or will it switch on again when the smoke alarm deactivates.
It would be a bit daft if when the smoke clears the contactor drops back in again and the machine starts smoking again!
 
Ok,
To be clear you need to be building a power control panel that is completely seperate from the pump controls. The only link between the two is the power to the pumps / pump controls.

To quote EN 61508 you need to be designing a system that is de-engergise to trip. You need a feed from the alarm system that is live when the alarm is NOT sounding. The normaly open contacts, that are held closed by the feed from the alarm system shall be in series with the main contactor coil. You need separate push button to cause the contactor to pull in when the alarm has been cleared. The relay mentioned above is to be wired as per the stop button or guard interlocks as shown on Safety - Protective Measures and Complementary Equipment

It would be useful if you could also have some status indicators on your unit. A typical DOL motor control box with a box with relay to one side may work in this application.
 
Have you designed this to stay off until it is reset by a deliberate action, or will it switch on again when the smoke alarm deactivates.
It would be a bit daft if when the smoke clears the contactor drops back in again and the machine starts smoking again!

And some form of consumer alarm, they are going to love it if it cuts the pump out on a false alarm and they jump into a freezing pool.

PS. they may not hear alarm from plant room.
 

Reply to smoke alarm to cut out circuit in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock