show us how. us plebs can only do the < and >. and i can sometimes enter "a" without activating the caps lock.Or could be... Iz≥In≥Ib or Ib≤In≤Iz
(just showing off as I've just discovered how to do those symbols)
(still working on how to do subscript on here)
Yes, and put a couple if smiley emoticons on thd post as well!show us how. us plebs can only do the < and >. and i can sometimes enter "a" without activating the caps lock.
BS 7671 specifically stated that ceiling roses etc. can be connected to a circuit with a protective device rating not exceeding 16A, so yes - it's in black and white that you can do it.So when is over load protection needed? In theory you could run a lighting circuit of a 16amp breaker then as long as the cable is correct for 16 amps?
1.5mm cable on a 16a breaker will work perfectly fine. It's how they do it in some other countries.So when is over load protection needed? In theory you could run a lighting circuit of a 16amp breaker then as long as the cable is correct for 16 amps?
1.5mm cable on a 16a breaker will work perfectly fine. It's how they do it in some other countries.
Ah i didn't take into account any potential difference in fitting ratings. I continue to learn !some lighting accessories, switches and connections in the U.K. are only rated at 5/6amps...
that said even running at 15-16 Amos I doubt they would over heat
a) Where the circuit load is not limited to below the cable CCC by design, i.e. the user could plug in or dial up more load on the equipment until the cable is overloaded.So when is over load protection needed
So i'm presuming a fault on 6a stuff wouldn't spike sufficiently to allow the 16a breaker to detect it