Danmatt

DIY
Joined
Feb 24, 2021
Messages
7
Reaction score
2
Location
UK
Hi, needed an EICR for my house. An electrician has issued me with an unsatisfactory certificate. He's invoiced me for doing the survey but obvs work needs doing. If I don't get him to do the remedial work where do I stand with having a satisfactory certificate?

Also, the electrician has said "There is no RCD protection for circuits 1 & 2, the consumer unit is made from plastic". Yes, I have a plastic consumer unit which he has put at a C3, commenting "Consumer unit is not metal or installed in a non-combustible cabinet or enclosure, showing NO signs of thermal damage, located under a wooden or combustible public stairwell forming part of an escape route from a dwelling area." My CU is not under my stairs nor is it part of an escape route. It's in a room next to the front door with a door which closes. The front door is not the only access to the outside of my house - I have a back door too through my kitchen.

My quote for works says "Replace & install consumer unit for dual RCD 18th edition". Do I actually need to replace the CU for a metal one or can the RCD protection be put in place for circuits 1&2.

Not sure if any of this makes sense.
 
No you do not need to replace the CU. It is a C3. Sometimes automated editing of certs leads to such items being put in an EICR. You can get caught out by that if you don't read the cert before you send it out. There are pre made insertions on the software that produces the cert that can make these "mistakes" it is all about checking/reading through the cert before you fire it out. Check with the spark who did it and you might find he will amend the cert when he looks at it. Bottom line, there is no need to change the CU unless there are compelling reasons to such as C1/C2 related to the CU. Apart form that it is opportunism suggesting you must change it, and that is putting it charitably.
 
You don't have to have the same guys back. Any work done to remedy issues highlighted by the EICR should have an accompanying minor works. The failed EICR and the combined Mi or Works for remedials cancel out the unsatisfactory EICR but you may have to pay to get a cert reissued as satisfactory as it is unlikely a spark would trust another sparks paperwork.

No you don't have to replace it and yes it could be possible to retrofit an RCD to cover those circuits provided adequate space and spares for your current board (generally appropriate RCDs and a length of busbar or RCBOs to replace the MCBs)
 
Hi, needed an EICR for my house. An electrician has issued me with an unsatisfactory certificate. He's invoiced me for doing the survey but obvs work needs doing. If I don't get him to do the remedial work where do I stand with having a satisfactory certificate?

Also, the electrician has said "There is no RCD protection for circuits 1 & 2, the consumer unit is made from plastic". Yes, I have a plastic consumer unit which he has put at a C3, commenting "Consumer unit is not metal or installed in a non-combustible cabinet or enclosure, showing NO signs of thermal damage, located under a wooden or combustible public stairwell forming part of an escape route from a dwelling area." My CU is not under my stairs nor is it part of an escape route. It's in a room next to the front door with a door which closes. The front door is not the only access to the outside of my house - I have a back door too through my kitchen.

My quote for works says "Replace & install consumer unit for dual RCD 18th edition". Do I actually need to replace the CU for a metal one or can the RCD protection be put in place for circuits 1&2.

Not sure if any of this makes sense.
He's not saying it is, I think he's trying to say it's not. To make it clearer he should he probably should have stated '' showing NO sign of thermal damage, nor is it located''.
Are any C1's or C2's listed? If not, why not satisfactory?
 
He's not saying it is, I think he's trying to say it's not. To make it clearer he should he probably should have stated '' showing NO sign of thermal damage, nor is it located''.
Are any C1's or C2's listed? If not, why not satisfactory?
that's how i read it. it's ambiguous how it's worded.
 
remedials cancel out the unsatisfactory EICR but you may have to pay to get a cert reissued as satisfactory as it is unlikely a spark would trust another sparks paperwork.
The first spark needs to see the work had been done, but the spark doing the the work would need to produce the new test certs which will cost the op again.
 
It might be an idea to post up a picture of your consumer unit. We'll be able to tell you if it's possible to add an RCD.
[ElectriciansForums.net] EICR Unsatisfactory
[ElectriciansForums.net] EICR Unsatisfactory

[ElectriciansForums.net] EICR Unsatisfactory

[ElectriciansForums.net] EICR Unsatisfactory

[ElectriciansForums.net] EICR Unsatisfactory

[ElectriciansForums.net] EICR Unsatisfactory

@loz2754 I've snipped what I think you could need to see. Anything else is either a tick, LIM or N/A. Cheers!
 
Thanks for posting part of the EICR.
From what I can see, all of the C2 items can be addressed without necessarily changing the consumer unit.

I believe the electrician has correctly coded as C3 the plastic consumer unit, but is suggesting it be replaced, not because of it not being non combustible, but as it is probably the best means of achieving RCD protection where it is lacking.
I would agree with that recommendation.

The only C2 items I would disagree with are for circuits passing through a bathroom, and for circuits supplying a bathroom. These should both be C3 according to both Napit codebreakers, and Electrical Safety First Best Practice Guide 4.

As has been suggested, the RCDs could possibly be added to your existing consumer unit, but that's not possible to tell from where I'm sitting right now. ?
 
So far, no one has explained to the OP that C3s do not result in an 'unsatisfactory' result. C1s and C2s are the ones that matter.
That appears to be a fair, honest and thorough EICR. There are a number of issues preventing the issuing of a satisfactory report, but most of these could be dealt with by a day's work.
The only thing I disagree with (from here) is the need to replace the CU, but if I was there in person, I might change my mind on that.
 
If the electrician has put down a C2 for 4.4 (IP rating of CU), this is nothing to do with it being plastic as that is 4.5 which he has dealt with. Without being there we cannot see why he has coded it C2 so we cant say that it shouldn't be a code C2. You could ask him, but if I had coded it a C2 and advised a consumer unit change then I would have done so for a reason. It is potentially dangerous (and it is not financially viable to fill all the gaps compared to changing the CU) and needs changing asap.
 
Thanks for posting part of the EICR.
From what I can see, all of the C2 items can be addressed without necessarily changing the consumer unit.

I believe the electrician has correctly coded as C3 the plastic consumer unit, but is suggesting it be replaced, not because of it not being non combustible, but as it is probably the best means of achieving RCD protection where it is lacking.
I would agree with that recommendation.

The only C2 items I would disagree with are for circuits passing through a bathroom, and for circuits supplying a bathroom. These should both be C3 according to both Napit codebreakers, and Electrical Safety First Best Practice Guide 4.

As has been suggested, the RCDs could possibly be added to your existing consumer unit, but that's not possible to tell from where I'm sitting right now. ?
@loz2754 what, you have no crystal ball??? Thanks for your reply!
 
So far, no one has explained to the OP that C3s do not result in an 'unsatisfactory' result. C1s and C2s are the ones that matter.
That appears to be a fair, honest and thorough EICR. There are a number of issues preventing the issuing of a satisfactory report, but most of these could be dealt with by a day's work.
The only thing I disagree with (from here) is the need to replace the CU, but if I was there in person, I might change my mind on that.
@brianmoooore it's ok. I understand about C3 being akin to an advisory on an MOT failure ?
 

Reply to EICR Unsatisfactory in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
951
Hello James, Thanks for your message. The points you described are good news for my neighbour because as you mentioned he will just be able to...
Replies
4
Views
189
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
Here the BPG#4 is useful, it is not a statutory document at all, but it provides good guidance as to what can reasonably considered as C1/C2/C3...
Replies
11
Views
645
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks