People who are not sure of the Current IEE Regulations should seriously consider joining a scheme provider and use the Technical Help Phone Lines they provide.
why would you put a fused spure in line on a dedicated supply for a IMM Heater. Isolating at the db then allows for maintenance, .
I under stand this, what im saying is that you would use a 20 amp db pole switch and the protective devices at the ccu would be 16 amp.
this would also give local isolation, but you would still need to isolate the circuit as you may have a loose wire in the spur.
Wikipedia is a wonderful tool
Don't quite see the problem here.
Immersion heaters have been required to be permanently connected via a DP switch for about 30 years.
Malc
If its proved wrong and these immersion heaters are not of an insulated type then a double switch it is.
Section 554.3 relates to Water heaters having immersed (that's immersion heaters) and uninsulated heating elements (that's standard elements where the outer sheath is connected to earth).
It may well have been mentioned before but i cant see it water heaters fitted to a storage vessel in excess of 15 ltrs capacity should be supplied by its own circuit Immersion heaters should be supplied by a double pole switch with flex outlet complying to BSEN60669-1 or BSEN60669-2-4 , this is according to building regulations page 56 of the electricians guide to building regs , and if im not mistaken should not be connected to fuse connection units ,
Pushrod - Because it was your thread I hope you don't think I was trying to dig you out, I was just trying to play catch up lol
I'll try to keep up.