carrying on our eicr from last week in office block we found wrong polarity in small workshop on ring main i no unreal but question it looks like maintenace guys have been using appliances but surely the breaker would trip as soon as a load was put on to this wrong polarity ring main we have corrected the ring main now but the guys said they have had no tripping problems your thoughts please
No the OCPD wouldn't trip as current still flows, it would only trip and break the neutral connection if a overload occurred.
ok thanks dilb was going to check breaker wasnt faulty had it in my head that when you plugged appliance in it would trip surely there must be some danger in having wrong polarity
Yes there is danger, it is a C1 on a EICR, as if the OCPD trips the line cable remains live.
Does a c1 fault not have to recitifed there and then when you find it ? or the curciut isolated ?
No, not necessarily , If the client wants to fry his wife when nobody's around. The most you can do is to warn the client that there is a dangerous fault which must be rectified immediately. The client then gives you the go ahead to proceed, or not.
We as electricians are not sanctioned by legislation.. bonkers or what !
Section 3 of the Health and Safety at Work Act 1974 and the Electricity at Work Regulations 1989 effectively require them to endeavour to make safe, before leaving site and with the agreement of the user or owner, any dangerous conditions found in an installation.
It is not sufficient simply to draw attention to the danger when submitting the priodic inspection report. At the very least, the inspector must ensure that the client is made aware at the time of discovery of the danger that exists. An agreement should be made with the client as to the appropriate action to be taken to remove the source of danger (for example, by switching off and isolating the affected part of the installation until remedied).
before continuing with the inspection or testing.
Dichroic
Dichroic
Yes, I agree with the first part, the rest is your wish list......dream on.
If the client tells you to get lost then it matters not one iota what you think should happen
The most you can do is notify the client that their installation will 'fry them' if they do nothing about it. Then its up to the insurance companies and possibly the courts.....
Of course there is a danger in reverse polarity, that is precisely the reason why you should test for it at least twice, once as the last of your dead tests and then again as first of your live tests. In most cases you will have also checked for correct polarity when conducting safe isolation at the supply main isolator and when EFLI (Zs) testing your final circuits.
How did this happen ie you look along the neutral bar and see blacks and blues then 2 reds/brown and the same at the fuses 2 black/blues ?
Dichroic
We as sparks cannot force a client to do anything, nor can we complete work without their permission. More than once I have sent very strong letters to clients and also sent a copy by registered post to myself to cover my backside.
Wirral
Business Name
Farm electrics
wrong polarity
Farmelectrics,
the pict,