1. Anyone who thinks this is about how to use a voltage indicator has completely missed the point and not understood the problem.
2. Anyone who thinks they know what they're doing by doing standard unaugmented safe isolation, on a board with a dead supply that may become live, needs to review their practice.
3. Continuity test proves the main switch is open and will withstand (typically) 24V. Repeat, 24V. Check your meter's low ohms range spec if you don't believe me. Air gaps do not obey Ohm's Law. Why bet your life on the hope that it will do the same at the peak voltage of 230V ac rms, when you could be sure by IR testing it which takes the same time? What you want to be sure of is that you are insulated from the supply. Big clue there.