Hi all

Any of you know whether there is a table or other source (other than waiting on hold for ages or opening the fuse covers)to find the short circuit capacity for a 200A main fuse in a 3 phase 40 year old supply?
Also is it going to be BS88 or 1361?
 
If they have tags then it is likely to be BS 1361 and if they are bullet fuses then BS 88

If they are most likely to be the old BS 88-2-2 or BS88-6 they could be 3000+ for 0.1 seconds but that type of fuse would most likely be for distribution and could be as low as 1200.

If they are 1361s then you really need to be contacting the manufacturers for their SC ratings
 
If they have tags then it is likely to be BS 1361 and if they are bullet fuses then BS 88

If they are most likely to be the old BS 88-2-2 or BS88-6 they could be 3000+ for 0.1 seconds but that type of fuse would most likely be for distribution and could be as low as 1200.

If they are 1361s then you really need to be contacting the manufacturers for their SC ratings

Hi Malc

I thought 1361 stopped at 100 amp?
 
Hi Malc

I thought 1361 stopped at 100 amp?

Hi Chr!s I think you could get 125amps at one time mate ................ and that is why I said most likely BS 88 either the 2.2 or the 6.

Saying that I have never seen a 1361 over 100amp but I'm sure at the pit they used 125 amps, but I stand corrected mate or they may have been to a different standard

I know the old Regs only went up to 100amp 1361 but there is something in my mind saying 125, but there again there is a lot in my mind that is rubbish lol
 
Hi all

Any of you know whether there is a table or other source (other than waiting on hold for ages or opening the fuse covers)to find the short circuit capacity for a 200A main fuse in a 3 phase 40 year old supply?
Also is it going to be BS88 or 1361?


We only used BS88 J type fuses in any service over 100A the BS1361 cartridge fuses being used for domestic and small services ie 60A and 100A

Iv1e just dug down to the bottom of my old toolbox and found a 200A which is rated at 80kA

As a point of interest no one would know what fuse rating is in a cut out as this was not recorded on our paperwork, so a 4ooA service head could have fuses from 400A down depending on the declared load at the the time of metering
 
We only used BS88 J type fuses in any service over 100A the BS1361 cartridge fuses being used for domestic and small services ie 60A and 100A

Iv1e just dug down to the bottom of my old toolbox and found a 200A which is rated at 80kA

As a point of interest no one would know what fuse rating is in a cut out as this was not recorded on our paperwork, so a 4ooA service head could have fuses from 400A down depending on the declared load at the the time of metering

Do you mean that the only way to know is to open the head?
 
Do you mean that the only way to know is to open the head?

That is up to the individual, all i would say is that any data enquiry to the dno results in a standard answer which sometimes could be correct and a lot of times will be wrong,so I guess the answer is yes, but with caution, if the cut out is plastic not too bad, but if it is the ironclad green ISCO then be very careful as carriers are porcelain and sometimes the thumbscrews are missing leaving a live part exposed
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
200A OPD 3 phase short circuit capacity
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
buttonmoon,
Last reply from
topquark,
Replies
14
Views
8,764

Advert

Back
Top