If I was replacing an existing light fitting in a domestic premises, making no alteration or addition to the circuitry, would I then be obligated to provide that circuit with 30mA RCD protection if it didn't already have it?
 
If it’s a “like for like” swap, then there’s no need to install an RCD, but you could just mention it to the customer and explain it would increase the safety of the circuit inline with the current regs.
 
I think the purpose of the regulation is that this is a job that is highly likely done by the householder or DIY'er and therefore gives increased protection. I think that it applies to new and rewired domestic lighting circuits for when the householder goes to change a standard pendant fitting to a decorative one. For RCD protection to be required on an existing installation when the householder wants to change a fitting would be costly and in most cases impractical. And in this case, the risk is reduced as it is done correctly by someone engaged that is competent.
 
Yes as I would carry out basic inspection and testing to ensure the circuit is safe and fit for continued use.
Fair enough, when replacing accessories or light fittings like for like, I usually make a note of a Zs and or any RCD test readings etc. where applicable on the job sheet for my reference, I don't normally go as far as issuing a MWC to the client but maybe I should start...?
 
Fair enough, when replacing accessories or light fittings like for like, I usually make a note of a Zs and or any RCD test readings etc. where applicable on the job sheet for my reference, I don't normally go as far as issuing a MWC to the client but maybe I should start...?
Completely up to you. Either method suits as all the client will do is shove it a drawer and forget about it.
 
I don't think many customers would give a stuff about a MW cert for a pi$$y --- little job, 15 minutes to put up the B&Q special, and another half an hour to gather the plethora of info now needed for a MW.
"That bit of paper is going to cost you another 20 quid labour Sir, that OK? Just chuck it in the bin when I've gone."
 
If I was replacing an existing light fitting in a domestic premises, making no alteration or addition to the circuitry, would I then be obligated to provide that circuit with 30mA RCD protection if it didn't already have it?
How would you do that if you are mot changing it to a dual RCD split one?
Unless if you fit an RCCBO on that cct.
What would you do with the other ccts in the board wjich are not RCD protected?
Sorry for the rant but you don't have to.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

spud1

Arms
-
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
30mA RCD protection required for existing circuit?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13
Unsolved
--

Advert

Thread statistics

Created
spud1,
Last reply from
Norah Nabino,
Replies
13
Views
3,597

Advert

Back
Top