On the side is a linking pin to the mechanical system of the ajoining breaker .... if it trips it then trips its adjoining mcb, its like a mousetrap - just needs a slight pressure to activate the trip.
The linking bar on the top where you operate them couldn't physically open the other breakers as it requires too much force ... the mcbs will all trip whether or not this switch bar was on or not.
Come on , fess up
what your really asking is can you retro bodge 3 single modules that you already have , into 1 3pole device cos the wholesalers are trying to spank you over the cost of a proper unit.
i can smell a scam a mile away lol.
And you could use 3 different amperage off breakers too.
One for a shower, one for a fan and one for a shaver unit.
Only playing, reference a recent thread.
Boydy
I had a similar thing on an EICR last year.
3 phase, the link between the breakers was broken, so 2 phases would go off, then you would have to flip off the other one separately.
I wasnt quite sure if I should give this a code.
I asked on the IET forum. The replies were "make an observation, not potentially dangerous".
Think of fuses supplying 3 phases - 3 separate fuses to take out, just like 3 separate CB's.
It isnt good practice to put a new install in with 3 separate CB's, but I cannot see it breaking any Regs.
You little tinker, can't believe MDJ ended up getting banned but the thread did get a bit heated
I had a similar thing on an EICR last year.
3 phase, the link between the breakers was broken, so 2 phases would go off, then you would have to flip off the other one separately.
I wasnt quite sure if I should give this a code.
I asked on the IET forum. The replies were "make an observation, not potentially dangerous".
Think of fuses supplying 3 phases - 3 separate fuses to take out, just like 3 separate CB's.
It isnt good practice to put a new install in with 3 separate CB's, but I cannot see it breaking any Regs.
Make an observation? - If the 3 separate mcbs are feeding a 3 phase motor and one trips (for whatever reason) then the motor may continue running on the remaining phases ('single phasing') - this can/will cause damage if left unnoticed.
But what if the motor was protected by 3 separate BS 88 fuses as most are would you code 3 That ?