Having a few issues with our alpha boiler 4years old, had a bit of bother with it last year in the back end towards summer, no issues over summer months, now the cold weather has started, its started tripping again. Then again no heating has been on over the summer!

Recent consumer unit change, from old dorman smith series 17 with dual RCD, never had any issues with it tripping those.

The boiler is virtually right next to the consumer unit,16A rcbo 2.5mm twin and earth down the back of the wall behind C/U under the floor and back up clipped direct into a FCU, flex out to boiler, 3 amp fuse. Cable insulation test is clear.

Controls are wireless so no faults with control wiring.

The boiler does not drip when firing up, having a shower ect, we usually just go to the tap and have no hot water, to find RCD tripped.

Has anyone had similar issues, read a few post regarding condensation dripping into flue stat?

Thanks
 
Sounds like a bit a pain in the arse, I wouldn't fancy paying a plumber £££ to poke around aimlessly in the boiler. Does the installation method/location of the boiler require it to be RCD protected?
 
Hi, no I'm not getting a plumber involved! I'd rather delv into it myself to have a look

Because the cable passes within the wall cavity and under the floor, then I would say yes it does have to be RCD protected, but I am thinking on putting it on a 16A mcb off the main switch (high integrity consumer unit) as I don't fancy waking up to run down the stairs starkers and flick the switch back on because I'm freezing my b***s off!
 
Could you pull In a bit of bs8436 cable using the old then no need for the rcd protection? That's assuming the cables are less than 50mm from the surface. In an ideal world you would find out why its happening but sometimes you've just got to do what you can :)
 
I could just clip a bit of 6242Y completely surface, as both cu and boiler are under the stairs (I know not ideal but "aye been") and take it off RCD, but as you say would like to know why it's happening.

Why would it not do it with the old dorman smith, rcd not as sensitive (no testing was done on the old RCds)
 
It may be the pump or a zone valve as it seems to be triggered by the heating.
If you can test the cables it may help .
Water and RCDs don't mix well lol. Worse with a bit of heat to help it on it's way.
 
Am I not right in saying with a combi hearing and hot water is the "same components" or no pump when it is just hot water? Won't be any zone valves?
 
We never "catch it tripping" i.e. We can't make it do it, we just go to wash the dishes (or mum does) and there's no hot water.
 
And it is only when the heating is on ? Is the boiler on it's own circuit, likely if it is right next to the board.What else have you not used over the summer ?
 
Like I say, we can happily use the heating and hot water at the moment but it seems to be tripping more randomly in the last month, it has got colder and the heating has been switched on so either one has triggered it, but the heating does work most of the time without it tripping and does not happen immediately

Boiler is on its own dedicated RCBO
 
May rig a temp light off that same supply so you can see when it trips!
 
No, it's only feeding that, it was always on a 16A so remained on a 16A/2.5,


I was just thinking of rigging up a relay with buzzer on the N/C contacts so it came on when the rcd tripped, but put of by the idea of getting woken up late at night!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Alpha combi tripping rcbo
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
87
Unsolved
--

Advert

Thread statistics

Created
Rocboni,
Last reply from
darksideby182,
Replies
87
Views
11,195

Advert

Back
Top