I’m wondering if someone can tell me in the OSG or regs that it has the short circuit breaking capacity of overcurrent devices someone said it was table 7.2A but can’t find it anywhere
 
Thanks very much guys also quick question where do I find codes for types of wiring? I have found the codes for installation methods

Another pick of the brains I know earth bonding should be less than 0.05 ohms but where in the regs/osg does it state that?
 
Last edited:
Thanks very much guys also quick question where do I find codes for types of wiring? I have found the codes for installation methods

Another pick of the brains I know earth bonding should be less than 0.05 ohms but where in the regs/osg does it state that?
types of wiring usually bottom of schedule of test forms. and earth bonding is not 0.05 ohms. that's a myth. the 0.05ohms refers to the resistance between a bonding conductor and the pipe its bonded to ( i.e. across the bonding clamp)
 
I’m wondering if someone can tell me in the OSG or regs that it has the short circuit breaking capacity of overcurrent devices someone said it was table 7.2A but can’t find it anywhere

The short circuit capacity of circuit breakers will be printed on the circuit breaker and will usually be either 6kA or 10kA for mcbs but can be other values, mccbs and accbs will have higher ratings.
For fuses or other devices you'll have to look up manufacturers information.
 
just to hi-jack thread, did a EICR yesterday . proteus 3871 MCBs, am i right in thinking 3kA?
 
Now i have been forced to look in a book, there appears to be a range of values for 3871 mcbs, M1-9 equals 1-9KA. TBH the table is a bit useless in my job, i always end up looking at breaker or selecting a breaking based on MI.....
 
proteus 3871 MCBs, am i right in thinking 3kA?

The plug-in type were M3, but the normal DIN-rail type 2's I think were M6. The only breaking capacity I'd really trust them with would be to break in half, which seemed to be an unavoidable consequence of trying to install them.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Adam_92

Trainee
-
Joined
Location
luton
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
breaking capacity of overcurrent devices
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
Adam_92,
Last reply from
Lucien Nunes,
Replies
13
Views
4,048

Advert

Back
Top