2m from meter to breaker panel.What is the length of the service cable you are upgrading?
200 amp three 2/0 copper one # 6 ground or 4/0 aluminum both choices require a 2inch conduit sorryI am doing a 100 to 200amps (underground) service upgrade.
Can I use the existing 11/4” pvc pipe to run the 200amps rated wires?
What is the smallest size of wire I can use for the 200amps?
View attachment 52927Is (2) #2/0awg copper & (1) #6awg neutral copper ok?