hi Guys


any ideas what code you would issue (if any) for 3 phase neutral and earth circuit ran through two TW+E cables, the circuit is supplied via a 3 phase mcb (the blue of one cable is used as the L2, its ran through trunking throught its route,

i know its not good practice but is there anything actually against the regs doing so ??

if there is ! which code would you advise

thanks
 
Using T&E in such a manner to my mind would not warrent a code.
If the conductors are not identified correctly, then I'd apply a code C3.
 
Each part of a circuit shall be arranged such that the conductors are not distributed over different multicore cables, conduit, ducting systems, trunking systems or tray or ladder systems

This requirement need not be met where a number of multicore cables, forming one circuit, are installed in parallel. Where multicore cables are installed in parallel each cable shall contain one conductor of each line

That is the part that I think would snag it for me colin.
If if not who the bloody hell runs 2X T + E in a trunking as a 3 phase supply, must be Roy Rogers.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Code for 3 phase neutral and earth circuit ran through two TW+E cable
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
R4BOE,
Last reply from
Engineer54,
Replies
8
Views
5,281

Advert

Back
Top