I have a pump that has basically been ripped of a folding machine, no cable, instructions, diagrams left for me. What would the two black wires normally be used for. The motor is 3 phase, and the brass links are set for star so was thinking would they be the nuetral?
Any help and suggestions welcome
Pump Motor term box.jpg
 
Just been given a stack of papers in which there is a wiring diagram. It shows it as being a thermal sensor. Would this mean having to use a 6 core cable to the pump.

I'll scan the page in and post it.
 
The thermal switch is optional normally and allows for an extra degree of protection, if it wasnt wired in before i dont see reason to now although assuming the motor has overload protection already all the thermal cutout will do is cut power before damage is caused to the winding if say the motor ran too hot as the overload may not see this until the winding overheat, this could occur if the impellor was broken or the motor air flow was restricted by something hence it overheats, you have to way up the risk of this and the consequences if it occured.
Obviously the thermal switch needs to be part of the stop or e-stop circuit to shut the motor down.
 
Last edited:
Hi

the two black wires will be for a thermister which is built into the motor windings, for this to be used in your motor control circuit you will need a thermister relay which has a contact which the control voltage is disconnected to the control in the event the motor gets too hot and protects it from overheating, dropping out the motor contactor.
The pump would run without this safety feature but may overheat and fail for obvious reasons.
the three phase is wired in the normal way.
 
Nice one guys. Looking at the 2nd picture in post 4, am i correct in saying that the thermal overload will be taken back to terminals 32 and 33 in the machines wiring panel?
 
i dont think there is a 'normal', in our factory all control wiring is orange sheathed and this is what i would use for thermistor monitoring, a few points ive picked up using thermistor monitoring relays, if star/delta motor, ensure the control circuit doesnt allow the motor to restart in delta after cooling and ive found it beneficial to wire a time delay so as the motor doesnt start as soon as the windings drop below the temperature threshold as 'cycling' will ocurr, ie, your winding temp will float above and below the thermistor cut out and stopping and starting the motor will aggravate your problem.
 
This may be a simple question to most of you but here goes. Looking at the diagram I have, it seem as though the wrong set of terminals are linked out (as supplied).

Which set would I connect my L1 L2 L3 to? The linked or the non linked?

Thanks again people
 

Reply to Connections to a pump motor. in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
686
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
689
Hi I'm having a problem with a 20 HP pump motor from a hydraulic press to try molds. When we energized the machine, it starts with star...
Replies
8
Views
2K
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi Experts, I was given a Ryobi 240v Table Saw which I think came from South Africa. The motor was disconnected when I checked but I would just...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock