If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician
How do we achieve a maximum automatic disconnection of supply time not exceeding 0.4 of a second, during a fault of negligible impedance to earth?
 
A fault of negligible impedance to earth is also known as a dead short to earth.

From ohms law, your very low resistance with a constant voltage gives an extremely high current.

The time graphs of whatever OCPD is in use as shown in the regs will mean an instantaneous trip. Well short of the 0.4s maximum.

And there is no longer EEBADS… it’s only ADS
 
Touch the neutral conductor.
 
I am trying to ascertain whether or not this forum has credibility, you may have quoted information to me that has been legally disclaimed by its' authors out of ignorance.
Which I can except.
Honesty, on the other hand, is a choice.
 
I could point you in the direction of a book published some years ago on earthing and bonding thar would probably confirm everything you are likely to say.
 
  • Funny
Reactions: freddo and Risteard
What happened when you touched the neutral conductor?
 
  • Like
Reactions: steve13
What happened?
I am not interested in reading anything else that has been legally disclaimed by its' author.
 
What happened?
I am not interested in reading anything else that has been legally disclaimed by its' author.

Which 'author' are you referring to here?
 
Any author(s) who legally disclaim(s) what they have written.
 
Post #2 is derived from legally disclaimed sources.
 
Post #2 is derived from legally disclaimed sources.

OK then. What are you saying is incorrect about post #2? Please reply with a proper answer though.
 
Post #2 is based upon the electrical wiring regulations written after the turn of the century, all of which have been legally disclaimed by their authors.
 
Post #2 is based upon the electrical wiring regulations written after the turn of the century, all of which have been legally disclaimed by their authors.

Come on Dave, you must know how to give proper answers by now at your age.

What is incorrect about post 2? And remember, I'm not asking who wrote it or where some of the origins are.

Please read my words twice before answering.
 
If you are ignorant of the fact that JPEL/64 has been legally disclaiming what it has written, I can except that.
 
  • Funny
Reactions: DPG
Touch the neutral conductor.
 
Line and neutral conductors are both live conductors, the response of the RCD will be exactly the same in either case.
 
Don't be rude and touch the neutral conductor.
 
Can't reach it
 
  • Funny
Reactions: freddo
There goes your credibility.
 
  • Funny
Reactions: Risteard
Touch the conductor.
 
Bearing in mind you asked a question originally, what is your answer to it? Or do you not know?
 
Making sure all of your earthing and bonding conductors are of a csa that is large enough to divert the earth fault current back to the mass of the earth, fast enough for your chosen overcurrent protective device to work within the specified time.
Have you touched the neutral conductor yet?
 
Thanks. I thought it would take longer than that to get a borderline reasonable response from you to be honest.

I may celebrate with a cuppa and a biscuit.
 
  • Like
Reactions: HappyHippyDad
I missed the end of Aryna because of you!
 
  • Funny
Reactions: DPG
I missed the point of this entire thread.


Any more incoherent trolling, and this thread is binned.

Signed, the author of #2
 
  • Funny
Reactions: DPG
(Q) - What happened when you touched the neutral conductor?
(A) - Nothing.

Conclusion:
The theory of 'ADS' is a legally disclaimed 'myth'.

Binning this thread would confirm that this forum has no credibility at all.
 
Last edited:
Binning the thread only confirms we don’t tolerate nonsense.

Where did “touching the neutral” come from? Wasn’t mentioned in the OP, which is from what #2 was referring to.
 
You got straight onto the subject of ADS, so I decided to skip straight to discrediting ADS.

I wasn't looking for an argument and ADS is just a myth, so why bother arguing about it?
 
Lives (as well as your credibility) are at stake, I am not going to talk any nonsense.
 
As I illuded to "if you were unaware that you have been spreading legally disclaimed 'propaganda'", I can except that.
But you have to wise up fast.
 
There appears to be some history under a different username, so i am going to stop this thread for now.
 
Status
Not open for further replies.

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cheltenham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Status
Not open for further replies.
Title
EEBADS
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
33

Thread Tags

Tags Tags
earth

Advert

Thread statistics

Created
DWCOCKBURN,
Last reply from
littlespark,
Replies
33
Views
543

Advert