bigspark17

-
Arms
Hi guys/gals… just pondering a gennie set up in a domestic that has a double pole changeover switch with 25mm tails in from dno and 25mm out to cu, 4mm cable then supplies the gennie male socket. Two queries i have, should the 4mm t&e have overload protection (all be it would be downstream)? And should there be a supplementary earth spike & 10mm connected to the met?

thanks
 
Last edited by a moderator:
The generator output should have OCPD anyway, and as long as nobody does something stupid like make up a 63A plug from a 15kVA generator to 32A or 16A socket feeding your plug & 4mm then I can't see much issue there. If you have any doubts about that sort of thing happening, then putting in a 32A MCB or similar fused-switch would solve it.

But you must have your own Earth provisions for the generator! You cannot assume the supply earth will be present during any sort of fault/outage as the whole supply cable could have been JCB'd. Most generators have 30mA RCDs (if socketed outputs, etc) so the rod below 200 ohm is not going to be too hard to meet but as always if you can safely drive in a 2.4m rod it will be much better.

And yes, I would use 10mm bond for it even if it is not TN-C-S yet, as probably that will happen eventually.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

bigspark17

Arms
-
Joined
Location
wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Generator set up
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
bigspark17,
Last reply from
pc1966,
Replies
3
Views
1,341

Advert

Back
Top