soar

just trying to builded up my confidence, am going to do an insulation resistance test on my ring and the lighting cicuit, but on the ring their are build-in appliances eg. fridge,wash machine,hob and electric heater that cant pluged out. and the light their are two dimmer and 14 spotlight,how s the best way to do this test please,
 
m8 i could be shot down for this so please wait for a UK based member to come along . join L -N and put the clip on then put other clip on Earth set your tester to 250v and away you go Here in spain its called method number2 but knowing UK it bound to be 123345667hgbXcg sec 2 part 17 exp 22 on a friday method.
 
have to agree with paella, LOL. you don't want to be putting 500V across L&N with appliances connected. but, don't these appliances have double pole isolation? as for the lights, remove all lamps, bridge the dimmers, and you can test normally.
 
when you say built in do you mean on a fused spur? You can isolate the aplliaces at the fuse spur and then IR the rest of the intallation and just note that on the cert as another option
 
I believe we also call it method 2.
The 250V test voltage would be used to test between all conductors as per method 1, as the equipment would routinely be subjected to such voltage.
If you link L & Ndue to voltage sensitive equipment, you would use 500V to test.
 
This is why you cant do a PIR tests in an Hr, you have to take your time. as said remove and refix takes up most of your time, but it has to be done, never rush or you might just get it wrong.
 
when you say built in do you mean on a fused spur? You can isolate the aplliaces at the fuse spur and then IR the rest of the intallation and just note that on the cert as another option

they plug in behind all the cupboard in the socket, no spurs. the only that have the isolater above the worktop is the oven
 
m8 i could be shot down for this so please wait for a UK based member to come along . join L -N and put the clip on then put other clip on Earth set your tester to 250v and away you go Here in spain its called method number2 but knowing UK it bound to be 123345667hgbXcg sec 2 part 17 exp 22 on a friday method.

am in the process of taking my 2391
 
have to agree with paella, LOL. you don't want to be putting 500V across L&N with appliances connected. but, don't these appliances have double pole isolation? as for the lights, remove all lamps, bridge the dimmers, and you can test normally.

are their any other way other than to remove the 14 lamp
 
nope.... unless they are elv, then you will have to dis the trannies.
 
are their any other way other than to remove the 14 lamp
Yes, link L & N together, (I usually use a 30A terminal block) and test to earth.
Oh yes, make a note on the PIR about the test method.
 
but only for testing phase conductors to E. if he wants to test P-N, then he's got to remove them.
 
so still did not get a definate answer, on the ring unplug what i can and then at the ccu link L & N and test to E at 250v dc
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
HELP !! with Insulation resistance test on ring and lighting circuit
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
soar,
Last reply from
soar,
Replies
28
Views
15,932

Advert

Back
Top