I was at a Job earlier today,the customers upstairs lights would not turn on due to the 6A mcb operating so it's a short circuit so I disconnected the supply to the first light the supply disconnected from consumer unit ,then did a insulation resistance which came out clear tried the mcb without any connection it stayed on.so connected the supply at consumer unit and left the other end not connected to anything it stayed on so connected the loop out and switch live it all come back on for 2 poxy minutes then it would come back on .I had to leave disconnected and will be returning back tommorow . Any suggestions would be extremely grateful
Thanks
 
You will just have to keep breaking the circuit down and testing it until you find it. Has any work been done recently? Anyone tried changing a light fitting ect? Banging in nails? Screwing up picture hooks etc?
 
Use the logical process with appropriate testing to find the fault.
Repair the fault.
Replace the MCB at your expense as you are likely to have damaged it by repeatedly closing it onto a fault.

Or

Employ the services of an electrician
 
  • Like
Reactions: 5 people
You claim to have 2330 level 3 nvq/AM2 /17th edition and your method of fault finding is to keep closing the MCB.

By the time you find the fault the MCB will be toast. That’s if the house hasn’t burnt down first.
 
basic fault finding this split the circut do your dead testing not trying mcb each time i would gather it will be simple to find
 
Dead testing is the basics of any fault finding, or even a new installation......start by breaking the circuit down until the fault is found. Instead of hit and missing with the mcb.
 
Not sure what to really say here tbh, this is your standard testing for a fault set-up and basic at that. I'd expect a trainee to ask a question like this but not someone who carries your qualifications.

Qualifications aside have you any practical experience in fault finding and when you did your apprenticeship were you not shown and/or taught how to, as Tony points out closing the protective device repeatedly onto the fault as part of your testing procedure shows you really don't know what your doing, use your meters they are there to safely identify the fault without you damaging your protective device or sending multiple mains transients into the network and upsetting other users on the same sub-station.
 
From what you describe you have not mentioned closing any switches when IR testing, so this sounds like a good palce to start since if the fault is (as is likely) at a light fitting and the switch is open then the fault will not show up.
Similarly if there are two way lights swap the switches while testing.
 
  • Like
Reactions: 1 person
Hi,

As Richard says , check the strappers on the 2 way. Had one a while ago at my brothers, tested fine, switched the 2 way; screw through the strapper and earth!

Regards.
 
It's pretty much been covered by the Guys already so just learn to fault find with your test equipment and leave the Bang test alone.
 
There’s always copper links, they usually finds the fault. Probably blow a hole in the ceiling but at least you’ll know where the fault was.







Was being the operative word.
 
Hello sparks
I was at a Job earlier today,the customers upstairs lights would not turn on due to the 6A mcb operating so it's a short circuit so I disconnected the supply to the first light the supply disconnected from consumer unit ,then did a insulation resistance which came out clear tried the mcb without any connection it stayed on.so connected the supply at consumer unit and left the other end not connected to anything it stayed on so connected the loop out and switch live it all come back on for 2 poxy minutes then it would come back on .I had to leave disconnected and will be returning back tommorow . Any suggestions would be extremely grateful
Thanks
You shouldn't have left it on for 2 poxy minutes, you should know that as a professional electrician.
It gets worst, sorry if that offends, not lol.
 
Yorkshire doesn’t exist as far as I’m concerned.


Herhmmm!!!! Its the preverbial Gods country but been an Atheist all I have as input is; 'there is Yorkshire and then there is the rest of the world'...... How very dare you :boxing_smiley:
 
Yorkshire-Terrier.jpg
 
  • Like
Reactions: 1 person
Thanks for most of the replys it ended up being a squished cable in the loft from a walk board on to and the c/u was not up to date to the 17 th edition 7671 so replaced with rcbos.tested dead and live test all performed and passed and certified and logged on to building control .so there won't be any house fires reported from Faversham .I thought I was on a site where I could talk to people in confidence without having the **** taken .I was wrong with my fault finding procedure I shouldn't of tried the mcb with a fault in the circuit but before I left I made sure it was all completely 100% safe hasn't any of yous been on a job and had to leave it and come back the next day with a clearer head obviously not cos you are all pefect.so thanks for your input keep it up north a .
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
mcb keeps blowing on lighting
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
74

Advert

Thread statistics

Created
Wayne Hudson,
Last reply from
Tuttle,
Replies
74
Views
7,704

Advert