where the other measures of 7671 522.6.5 are not used and a cable passes through a joist less than 50mm from the top, the cable must have adequate mechanical protection against nails, etc. Please tell me, does this requirement only apply to the parts of the cable passing through the joist? or does the entire length require mechanical protection? so can the part of the cable that protrudes out be left unprotected? The most likely place a nail would be inserted is in line with the joist to fix the floor boa

If the cable requires protection along it's entire length anywhere within 50mm from the top, why does the regulation specifically mention joists? they could have just said more generally, anywhere a cable is within 50mm of a floor or ceiling it must be protected. also the safe plates used to protect cables in notches only cover the joist itself, so the protruding part of the cable could still be damaged by a nail if someone decided to put nails randomly away from the joist.
 
Last edited:
i would say just where it goes through the joist and it needs to be a 3mm steel plate or summin like that. IMO HTH
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Mechanical protection through joists
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
bureaucrazy,
Last reply from
m4tty,
Replies
1
Views
3,114

Advert

Back
Top