A customer wants a consumer unit moved about a meter to one side, because she's converting the garage and wants to put a door where the consumer unit is now.
If I don't upgrade the consumer unit, and don't alter or add to any of the circuits, do I have to test the whole house and give an Installation Certificate?
 
I would be testing, what happens if someone gets a fatal belt a few weeks after you moved it and you have no test results. It could be totally unsafe within the fabric.

I think the finger would be pointed straight at the mover....................
 
I would be testing, what happens if someone gets a fatal belt a few weeks after you moved it and you have no test results. It could be totally unsafe within the fabric.

I think the finger would be pointed straight at the mover....................

so you carry out a full EICR for every job ?
 
so you carry out a full EICR for every job ?

I think you obviously have to exercise common sense but yes in this case I would as there is going to be other electrical work carried out to convert the garage into a useable room which would require building regs for change of use.

Other factors need to be considered like age of installation, diy work apparent etc etc
 
Personally I'd treat it as a CU change from the testing point of view.

so you carry out a full EICR for every job ?

No, only the ones where I disconnect every circuit for the installation, extend the cables, then make new connections. It just wouldn't seem right not to.
 
This sounds like a partial rewire :)
Every circuit is getting a new bit of wiring, I am not sure you can still use the "old" board at all.
No need to do an EICR for every job, but the ones where you are altering the Zs and R1+R2 of all the circuits, should in IHMO be tested up front and a Installation cert done afterwards, how would you know if you have increased the VD beyond what is acceptable?
 

Reply to Moving the CU in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top