Hi i have been approached by a customer who wants a metal light fitting (obvious needs a cpc) but the wiring is from the 60s and they only installed twin L+N. If i run a CPC from a socket in the room up to the light fitting is this acceptable?
 
The cpc should follow the route of the cable for which the cpc applies and would need to be 4mm if unprotected.
Best to run a cpc from the CU along the circuit to the fitting (and cover the light switch as well!)
 
as above^^^ or you don't do the job.
 
Don't forget 30mA protection and Boding etc lol

What a load of effort for a bloomin light fitting... Soon see how much they like it when they look over your quote;)
 
Hi i have been approached by a customer who wants a metal light fitting (obvious needs a cpc) but the wiring is from the 60s and they only installed twin L+N. If i run a CPC from a socket in the room up to the light fitting is this acceptable?

The problem with doing it the way you have suggested, there is no R1 & R2 from the DB's lighting circuit to that metal fitting ( although it is earthed from the sockets). Best to run a seperate cpc or get a different fitting as others have said.
 
So is that document saying that you can fit class 1 fittings without a CPc asking as an ir value over 1Mohm is achieved? And an RCd is fitted !!!
 
So is that document saying that you can fit class 1 fittings without a CPc asking as an ir value over 1Mohm is achieved? And an RCd is fitted !!!

No, it's advising on a CU change where there is existing class 1 fittings and the client refuses to replace/rewire.
 
Ok so say you do a cu change then are they saying that you can leave the class1 fittings fitted!!
 
only if the fitting is not simultaneously accessible with earthed metal parts. personally , i would not like to use that argument in front of a judge and jury.
 
only if the fitting is not simultaneously accessible with earthed metal parts. personally , i would not like to use that argument in front of a judge and jury.

No neither would I but I am trying to find a way to justify it in my head but I just can't seem to be able to!
 
No neither would I but I am trying to find a way to justify it in my head but I just can't seem to be able to!

There isn't any real justification of allowing Class1 lighting fittings on a Class11 circuit. This is just another cover all situation where an RCD is being used to replace a non-existent ADS. Seems even the powers at be, can so easily forget that RCD devices are supposed to be ''Additional'' Protection, and not a Primary protection on TN installations!!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
No CPC on the lighting circuit but the customer wants a metal fitting!!
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
thwaitpd,
Last reply from
brman,
Replies
25
Views
4,622

Advert

Back
Top